Subject: |
[Fwd: COMMUNICATION between EPICS and the Allen Bradley SLC 500] |
Marty Kraimer <[email protected]> |
To: |
[email protected] |
Date: |
Thu, 29 Aug 1996 07:33:23 -0500 |
--- Begin Message ---
* The Equipment Protection System (EPS) Status will be sent to EPICS via a
6008-SV1R VME Allen Bradley Remote I/O Scanner. The scanner (i.e. a
6008-SV1R) actually talks to the SLC 500 remote I/O via a Direct
Communications Module (i.e. a 1747-DCM). The DCM module has an input image
table and an output image table. Each table contains eight 16-bit words.
The first word in each table is reserved for the status word. The
remaining seven words are used for data. Implementing ladder logic for the
DCM is very simple and is described in the user manuals. However, VME
scanner is implemented with EPICS and is not so straight forward on how
data is actually getting captured. Apparently we are only able to choose
AB-Binary input device type in EPICS. This device type apparently reads
8-bit chunks of data. This means that the first 8-bit chunk is denoted by
card 0, the second 8-bit chunk is denoted by card 1, and so on and so
forth. So far, things are working great as long as I choose AB-Binary
input device type. Therefore the questions is how are the other Allen
Bradley (bi) device types used ?
ANSWER: Since most SLC 500 Chassis can be set up as "1- slot
addressing" one can use the scheme on page 5 of the EPICS: Allen Bradley
Driver and Device Support documentation. This documentation can be found
at URL address:
(http://www.aps.anl.gov/asd/controls/epics/EpicsDocumentation/WWWPages/H
ardwareNoFrame.html#Allen_Bradley)
When using the 1747-DCM the formula used for card selection in gdct is as
follows:
Card = word*2, where word corresponds to one of the eight words in the
DCM's output image table.
Signal = bit location within the word.
Since each word in the 1747-DCM is 16 bits, it makes since to use the AB-16
bit BI device type in EPICS.
This works great now.
Marty Kraimer, Mark Rivers, Josh Stein, and Chris Seavers were all
instrumental in helping me resolve this issue of how to make EPICS talk to
my SLC 500 Chassis.
Advanced Photon Source
MHATT-CAT
(630)252-0209
Ernest
P.S. Marty can you forward this on to "tech talk"
--- End Message ---
IDL Widget builder S. Joshua Stein
Opening at Jefferson Lab (aka CEBAF) watson
<1996>
Re: [Fwd: COMMUNICATION between EPICS and the Allen Bradley SLC 500] Nick Rees
<1996>
ANJ, 10 Aug 2010 |
Home
News
About
Base
Modules
Extensions
Distributions
Download
Search
EPICS V4
IRMIS
Talk
Bugs
Documents
Links
Licensing
