Subject: Re: Asyn GPIB proto file exception @writetimeout
To: <jlarsson@triumf.ca>
Cc: EPICS <tech-talk@aps.anl.gov>
Date: Fri, 20 Oct 2017 11:56:56 +0200
a) Disable error handlers during @init. This is the easy way out.
In StreamCore.cc method finishProtocol(ProtocolResult status)
find the line
    if (runningHandler)
and replace it with
    if (runningHandler || flags & InitRun)
Then @writetimeout will not be called during @init, only later during periodic processing. But at least it will not crash.
Maybe it is better not to use @init for this purpose but instead set field(PINI, "YES") in the record. @init was meant to read start values for output records because this needs a different protocol than normal processing.
Dirk
On 20.10.2017 11:39, Dirk Zimoch wrote:
Hello James,
I could reproduce your problem with an Agilent E5810A Lan/GPIB gateway
and no device connected.
The crash happens only when @writetimeout is triggered during @init and
executes dbpf. If one of the three prerequisites is not fulfilled, it
does not crash.
Thus I guessed calling dbpf before iocInit finishes is the actual
problem. I checked that theory by simply adding the following line to
the startup script before iocInit:
dbpf HEBT:SCOPE1:ALIVE.A 1
It crashes.
Thus the crash is not directly related to StreamDevice but to the fact
that dbpf is called on a not yet fully initialized database.
I need to investigate how I can fix the problem. I have two options in
mind:
b) Run @init later. At the moment, it is run during init_record. Other
records may not have been initialized at this time. Maybe I can move
@init to a later time using initHooks.
Dirk
On 20.10.2017 10:52, Dirk Zimoch wrote:
Hi James,
How is your GPIB device connected? Do you have a GPIB card or do you use
a LAN-GPIB box (which model?) or does the device itself have a vxi11
(GPIP over TCP) interface? In your mail I could not see how the asyn
port is created. Do you use vxi11Configure?
If you use a LAN-GPIB box, is the box running when the device is offline?
Dirk
BTW: When I replied on your first tech-talk mail on Oct 6, I got an
error from your mail server: "<jlarsson@triumf.ca>... Account disabled
05/Oct/2017"
Seems to be fixed by now.
Dirk
On 19.10.2017 21:02, jlarsson@triumf.ca wrote:
Hey there,
Thanks for taking a look.  The theory and practice I use the ASYN /
StreamDevice for is as follows.  I use the an IDN record and function to
query the device name, once every 10 seconds. In an Agilent WFG for
example. I have a separate periodic scan record that queries/sets the
device qualities.
In the IDN portion of the proto file I execute a 'dbpf SOMERECORD 1'
and a
reply timeout exception of 'dbpf SOMERECORD 0'.  It acts like a ping. I
then use that bit in epics to drive the DISV / DISA / SDIS, of a common
scan record.
So if my Agilent WFG is turned off, then I stop trying to read/write the
device qualities. But the IDN still checks.  So if someone comes and
turns
the WFG on, epics starts reading and writing the qualities again.
It's nice because it cleans up unnecessary (and polled typically)
network
traffic as well limits the number of error messages generated, and
lastly
stops an IOC from processing things unnecessarily.
I tried this with GPIB devices, but I don't get exception code called in
the proto file.
Here is the record text that is relevant, I can send you attached
complete
ones if you like.  The ALIVE record referenced below in the proto is a
simple calc record.
[ the record .... ]
record(stringin,"HEBT:SCOPE1:IDN") {
    field(DESC,"string input record")
    field(SCAN,"10 second")
    field(PINI,"YES")
    field(PHAS,"0")
    field(EVNT,"0")
    field(DTYP,"stream")
    field(DISV,"1")
    field(SDIS,"0.000000000000000e+00")
    field(DISS,"NO_ALARM")
    field(PRIO,"LOW")
    field(FLNK,"0.000000000000000e+00")
    field(VAL,"string")
    field(INP,"@tektds8000.proto IDN(HEBT:SCOPE1) GPIB0 10")
    field(SIOL,"0.000000000000000e+00")
    field(SIML,"0.000000000000000e+00")
    field(SIMS,"NO_ALARM")
[ the proto that fails to call the exception exec.... ]
IDN {
    InTerminator = LF;
    @init {
        out "HEADER OFF";
        out "*IDN?";
        # in "%s %s";
        in "%64c";
    out "*IDN?";
    # in "%s %s";
    in "%64c";
     # Added by James Larsson Oct. 5 2017 to throttle ASYN Error
Messages
     exec "dbpf \$1:ALIVE.A 0";
     @replytimeout
        exec "dbpf \$1:ALIVE.A 1 ";
[ the proto that crashes the IOC (just a @writetimeout delta).... ]
IDN {
    InTerminator = LF;
    @init {
        out "HEADER OFF";
        out "*IDN?";
        # in "%s %s";
        in "%64c";
    out "*IDN?";
    # in "%s %s";
    in "%64c";
Messages
     @writetimeout
[The script portion that configures the GPIB device: and the '.....'
are mine
asynSetOption("GPIB0",10,0x0c,0)
asynSetTraceIOMask(GPIB0,10,0x0005)
asynSetTraceMask  (GPIB0,10,0x001f)
dbLoadRecords("asynRecord.db","P=HEBT:SCOPE1:,R=ASYN,PORT=GPIB0,ADDR=2,IMAX=0,OMAX=0")
asynSetTraceMask  (GPIB0,10,0x0000)
asynSetTraceIOMask(GPIB0,10,0x0000)
Cheers and Thanks again!
James Larsson, P.Eng.
Triumf Control Systems Engineer
Hello James,
I am back from ICALEPCS, thus I can start debugging your StreamDevice
problem.
In order to reproduce your problem, I need some more information from
you.
Please send me:
* The part of your startup script where you configure the GPIB device
* The record that causes the crash
* The protocol file used by this record.
Best regards,
Dirk
On 06.10.2017 17:40, jlarsson@triumf.ca wrote:
Hey hey!
I have a device on my Linux IOC, using Asyn GPIB.  The device works on
the
IOC and, connected with EDM - is controllable.
When the device is turned off I get an error message:  asynError in
write:
GPIB0 writeGpib failed ENOL 2: No listeners
The function in the proto file uses exception @replytimeout, but that
never executes,  which I would expect (I queried a device, it's not
there,
I should have a timeout). This works on TCP/IP devices, just not GPIB.
Does anyone have any thoughts, or hacks, or updates on getting GPIB
exceptions to run the proto file exception commands?
Also when I try using the @writetimeout exception to more closely
mimic
the error message, the IOC crashes on boot, not even an IOC command
prompt, which looks like a separate problem, any help on that would
also
be appreciated.  Error message is:
A call to 'assert(dbLockIsInitialized)'
    by thread 'cbLow' failed in ../dbLock.c line 239.
EPICS Release EPICS R3.14.11 $R3-14-11$ $2009/08/28 18:47:36$.
Local time is 2017-10-06 08:13:40.495885987 PDT
Please E-mail this message to the author or to tech-talk@aps.anl.gov
Calling epicsThreadSuspendSelf()
Thread cbLow (0x9a12518) suspended
Cheers
James Larsson
Re: Asyn GPIB proto file exception @writetimeout jlarsson
Re: Asyn GPIB proto file exception @writetimeout Dirk Zimoch
Prev: Re: Asyn GPIB proto file exception @writetimeout Dirk Zimoch
Next: Re: Asyn GPIB proto file exception @writetimeout jlarsson
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  <2017
ANJ, 20 Oct 2017 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·
· EPICS V4 · IRMIS · Talk · Bugs · Documents · Links · Licensing ·