1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  <20172018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  <20172018  2019  2020  2021  2022  2023  2024
Subject: Re: [AsynPortDriver] "Multiple interrupt callbacks between processing" warning with multiple arrays
Cc: [email protected]
Date: Tue, 11 Apr 2017 21:55:18 +0200
When you say "lower than 1 second" do you mean the time between
callbacks in your driver is less than 1 second, i.e. the usleep()
value is less than 1000000?
Exactly, value below 1000000 (well, actually I can get down to 600000 without warnings) in usleep results in warnings. Maybe it's a matter of speed, the machine that runs the IOC (and only the IOC, CSS is running on a separate computer) is not the fastest one, but our Qt application for this device is able to achieve update rate of ~100 ms at the same time drawing plot, so I think period in the range of 100-150 ms should be achievable here.
Now when I added asynSetTraceMask for the "missing" channels 1-3 now it reports this warning for all variables.
Kind regards,
Paweł
W dniu 2017-04-11 21:18, Mark Rivers napisał(a):
The record definition and dbpr output looks OK to me.
In your original post you said:
The driver works, however if the update rate is lower than 1 second,
strange warning appears in the console at the time of every refresh
(and  that's only for one of 4 channels), namely:
2017/04/11 15:42:08.682 PIEZO:OSC-CH0-WAVEFORM
devAsynFloat64Array::interruptCallbackInput
\000\000\000\000\000@\205?\000\000\000\000\000\300\202?\000\000\000\000\000\000\204?\000\000\000\000\000\000\204?\000\000\000\000\000\300\202?\000\000\000\000\000\000\204?\000\000\000\000\000@\205?\000\000\000\000\000\000\204?\000\000\000\000\000\300\202?\000\000\000\000\000\000\204?
Is the output coming because you have enabled some asynTrace?
devAsynFloat64Array::processCommon, warning, multiple interrupt callbacks between processing
Are you saying that this warning message only happens on the first
waveform record, not on all of them?  That message is printed with
this code in devAsynXXXArray.h:
            if (pPvt->gotValue) {
                asynPrint(pPvt->pasynUser, ASYN_TRACE_WARNING,
                    "%s %s::processCommon, "
                    "warning: multiple interrupt callbacks between
processing\n",                  \
                     pr->name, driverName);
Note that it is printed with the ASYN_TRACE_WARNING mask.  How have
you called asynSetTraceMask in your startup script?  Is it possible
you set it like this?
asynSetTraceMask(testAPD, 0, 255)
If so that would explain why you are only seeing the messages for the
first waveform record.  The asynTrace is specific to the asyn address,
and this only enables asynTrace on address 0.  To see the messages
from all 4 waveform records you can do this:
asynSetTraceMask(testAPD, -1, 255)
or this
asynSetTraceMask(testAPD, 1, 255)
asynSetTraceMask(testAPD, 2, 255)
asynSetTraceMask(testAPD, 3, 255)
This would not explain why you are getting the messages in the first
place, but it would explain why you are only seeing them for the first
waveform record.
-----Original Message-----
Sent: Tuesday, April 11, 2017 1:55 PM
To: Mark Rivers
Hi Mark,
thanks for quick answer. Actually I forgot to post the record, but it
had SCAN set to I/O INTR, similarly to the example project. Here's the
record definition:
record(waveform, "PIEZO:OSC-CH$(CHANNEL)-WAVEFORM")
     field(DTYP, "asynFloat64ArrayIn")
     field(INP,  "@asyn($(PORT),$(ADDR),$(TIMEOUT))OSC_WAVEFORM")
     field(FTVL, "DOUBLE")
     field(NELM, "$(NPOINTS)")
     field(LOPR, "0")
     field(HOPR, "10")
     field(SCAN, "I/O Intr")
As for the commands you asked for, the results are, respectively:
ACKS: NO_ALARM      ACKT: YES           APST: Always        ASG:
ASP: (nil)          BKPT: 00            BPTR: 0xbcb3e0      BUSY: 0
DESC:               DISA: 0             DISP: 0             DISS:
NO_ALARM
DISV: 1             DPVT: 0xc05690      DSET: 0x7f2dbdcea9a0
DTYP: asynFloat64ArrayIn                EGU:                EVNT: 0
FLNK:CONSTANT 0     FTVL: DOUBLE        HASH: 0             HOPR: 10
INP:INST_IO @asyn(testAPD,0,1)OSC_WAVEFORM                  LCNT: 0
LOPR: 0             LSET: 0xc07f40
MLIS: 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
MLOK: b0 b3 bc 00 00 00 00 00           MPST: Always
NAME: PIEZO:OSC-CH0-WAVEFORM            NELM: 1000          NORD: 1000
NSEV: NO_ALARM      NSTA: NO_ALARM      PACT: 0             PHAS: 0
PINI: NO            PPN: (nil)          PPNR: (nil)         PREC: 0
PRIO: LOW           PROC: 0             PUTF: 0             RARM: 0
RDES: 0xb86470      RPRO: 0             RSET: 0x7f2dbda73340
SCAN: I/O Intr      SDIS:CONSTANT       SEVR: NO_ALARM
SIML:CONSTANT
SIMM: NO            SIMS: NO_ALARM      SIOL:CONSTANT       SPVT:
0xc135e0
STAT: NO_ALARM      TIME: 2017-04-11 20:53:12.153366126     TPRO: 0
TSE: 0              TSEL:CONSTANT       UDF: 0              VAL: (nil)
ASP: (nil)          BKPT: 00            BPTR: 0xbcd3a0      BUSY: 0
NO_ALARM
DISV: 1             DPVT: 0xc05be0      DSET: 0x7f2dbdcea9a0
INP:INST_IO @asyn(testAPD,1,1)OSC_WAVEFORM                  LCNT: 0
LOPR: 0             LSET: 0xc07f60
MLOK: 70 d3 bc 00 00 00 00 00           MPST: Always
NAME: PIEZO:OSC-CH1-WAVEFORM            NELM: 1000          NORD: 1000
SIML:CONSTANT
0xc138f0
STAT: NO_ALARM      TIME: 2017-04-11 20:53:29.910249080     TPRO: 0
ASP: (nil)          BKPT: 00            BPTR: 0xbcf360      BUSY: 0
NO_ALARM
DISV: 1             DPVT: 0xc060e0      DSET: 0x7f2dbdcea9a0
INP:INST_IO @asyn(testAPD,2,1)OSC_WAVEFORM                  LCNT: 0
LOPR: 0             LSET: 0xc07f80
MLOK: 30 f3 bc 00 00 00 00 00           MPST: Always
NAME: PIEZO:OSC-CH2-WAVEFORM            NELM: 1000          NORD: 1000
SIML:CONSTANT
0xc13c00
STAT: NO_ALARM      TIME: 2017-04-11 20:54:17.907769453     TPRO: 0
ASP: (nil)          BKPT: 00            BPTR: 0xa7b540      BUSY: 0
NO_ALARM
DISV: 1             DPVT: 0xab0810      DSET: 0x7efec944b9a0
INP:INST_IO @asyn(testAPD,3,1)OSC_WAVEFORM                  LCNT: 0
LOPR: 0             LSET: 0xab21d0
MLOK: 10 b5 a7 00 00 00 00 00           MPST: Always
NAME: PIEZO:OSC-CH3-WAVEFORM            NELM: 1000          NORD: 1000
RDES: 0xa30650      RPRO: 0             RSET: 0x7efec91d4340
SIML:CONSTANT
0xabe140
STAT: NO_ALARM      TIME: 2017-04-11 20:52:33.970326348     TPRO: 0
Best regards,
Paweł
W dniu 2017-04-11 18:24, Mark Rivers napisał(a):
Hi Pawel,
What is the SCAN field of your waveform record?  I suspect it is
probably periodic ("1 second", etc.).  For this application you should
set it to SCAN="I/O Intr".  Then the waveform record will process each
time your driver does a callback to device support.  If the record is
periodically processing at 1 second and your driver is doing callbacks
faster than 1 Hz then you will see the error you report.
[mailto:[email protected]] On Behalf Of Pawel Plewinski
Sent: Tuesday, April 11, 2017 8:49 AM
To: [email protected]
Subject: [AsynPortDriver] "Multiple interrupt callbacks between
I've recently written asyn-based device support for a custom device
communicating over PCIe. One of its functions is to periodically
retrieve 4 waveforms from 4 channels, which is done in a separate
thread, from which the callback function is called to notify asyn about
change. I heavily based the code on the AsynPortDriver example.
(and
The parameters passed to the top level constructor are
    : asynPortDriver(portName,
                     4, /* maxAddr */
                     (int)NUM_SCOPE_PARAMS,
                     asynInt32Mask | asynFloat64Mask |
asynFloat64ArrayMask | asynEnumMask | asynDrvUserMask, /* Interface
mask
asynFloat64ArrayMask | asynEnumMask,  /* Interrupt mask */
                     ASYN_MULTIDEVICE, /* asynFlags.  This driver does
not block and it is not multi-device, so flag is 0 */
                     1, /* Autoconnect */
                     0, /* Default priority */
                     0) /* Default stack size*/
The readback thread code:
void piezoPortDriver::readbackTask(void)
    while (1) {
            bool stopped = false;
            lock();
            auto new_data = osc->fetch_data(vtim, vdat);
            unlock();
            if (!stopped)
                lock();
                this->osc_update_trigger();
                unlock();
         callParamCallbacks();
         for (int i = 0; i < 4; i++){
           doCallbacksFloat64Array(vdat[i].data(), vdat[i].size(),
P_OscWaveform, i);
         usleep(100000);
The fetch_data method reads four 1000-element double vectors from PCIe.
Could you give me some suggestions what may be wrong?
Paweł Plewiński
Department of Microelectronics and Computer Science
Lodz University of Technology
RE: [AsynPortDriver] "Multiple interrupt callbacks between processing" warning with multiple arrays Mark Rivers
[AsynPortDriver] "Multiple interrupt callbacks between processing" warning with multiple arrays Paweł Plewiński
Re: [AsynPortDriver] "Multiple interrupt callbacks between processing" warning with multiple arrays Paweł Plewiński
Prev: RE: [AsynPortDriver] "Multiple interrupt callbacks between processing" warning with multiple arrays Mark Rivers
Next: RE: [AsynPortDriver] "Multiple interrupt callbacks between processing" warning with multiple arrays Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  <20172018  2019  2020  2021  2022  2023  2024
ANJ, 21 Dec 2017 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·