1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024
Subject: RE: Kohzu motors poll rate issue??
To: "'Alireza Panna'" <[email protected]>
Date: Wed, 9 Mar 2016 17:03:21 +0000
Hi Ali,
I can see the problem.  Each poll consists of 3 write/read operations.
It writes the following 3 commands and reads the response to each.
\002RSY1/21
\002STR1/1
\002RDP1/0
The time between each write and the subsequent response is 12 ms, 17 ms, and 13 ms for the 3 commands.  These times are reproducible for the 2 poll cycles you showed.
Once a response is received the time to send the next poll command is always only 1 ms.
So the total poll time is 12+17+13+1+1+1 = 45 ms.  That means the poll frequency will be 1/.045 = 22 Hz, which is exactly what you see.
So the problem is not in the motor driver, the problem is your device.  It takes 12-17 ms to reply to each poll command.
Sent: Wednesday, March 09, 2016 10:47 AM
To: Mark Rivers
Cc: [email protected]
Subject: Re: Kohzu motors poll rate issue??
Hi Mark,
So i turned the asyn trace masks on:
#For debugging purposes
asynSetTraceMask("kohzu",-1,0x9)
asynSetTraceIOMask("kohzu",-1,0x2)
Here's the output that I see when I move the motor:
2016/03/09 11:25:15.013 kohzu addr 4 gpibPortRead
C\tRDP1\t-5428\r\n
2016/03/09 11:25:15.014 kohzu addr 4 gpibPortWrite
\002RSY1/21\r\n
2016/03/09 11:25:15.026 kohzu addr 4 gpibPortRead
C\tRSY1\t21\t0\r\n
2016/03/09 11:25:15.027 kohzu addr 4 gpibPortWrite
\002STR1/1\r\n
2016/03/09 11:25:15.044 kohzu addr 4 gpibPortRead
C\tSTR1\t1\t1\t0\t0\t0\t0\t0\t0\r\n
2016/03/09 11:25:15.045 kohzu addr 4 gpibPortWrite
\002RDP1/0\r\n
2016/03/09 11:25:15.058 kohzu addr 4 gpibPortRead
C\tRDP1\t-5384\r\n
2016/03/09 11:25:15.059 kohzu addr 4 gpibPortWrite
\002RSY1/21\r\n
2016/03/09 11:25:15.071 kohzu addr 4 gpibPortRead
C\tRSY1\t21\t0\r\n
2016/03/09 11:25:15.072 kohzu addr 4 gpibPortWrite
\002STR1/1\r\n
2016/03/09 11:25:15.089 kohzu addr 4 gpibPortRead
2016/03/09 11:25:15.090 kohzu addr 4 gpibPortWrite
\002RDP1/0\r\n
2016/03/09 11:25:15.103 kohzu addr 4 gpibPortRead
C\tRDP1\t-5338\r\n
The bold lines are when it is reading the co-ordinate value. You can see from here that the interval for subsequent reads is around 0.045s (~22Hz)
Best,
Ali
Alireza Panna
University of Maryland, College Park
On Tue, Mar 8, 2016 at 7:46 PM, Mark Rivers <[email protected]> wrote:
Hi Ali,
To help figure this out you can do:
asynSetTraceIOMask portName -1 2
asynSetTraceMask portName -1 9
portName is the asyn port name of the GPIB port.  -1 means all addresses.  2 means ASYN_TRACEIO_ESCAPE and 9 means ASYN_TRACE_ERROR | ASYN_TRACEIO_DRIVER.
You will then see all of the communication from the IOC to the controllers, with time-stamps.  So you can see if the problem is communications delays or something else.
You may want to send the asynTrace output to a file
asynSetTraceFile portName -1 “myTraceFile.txt”
From: [email protected] [mailto:[email protected]] On Behalf Of Alireza Panna
Sent: Tuesday, March 08, 2016 5:25 PM
To: [email protected]
Subject: Kohzu motors poll rate issue??
Hello tech-talkers,
I have 5 SC-410 motor controllers daisy chained to a NI PCIe GPIB controller. The motor controllers are used to control a total of 18 kohzu positioning stages. In the start-up file, I set up the kohzu controllers to poll at 60Hz
# Kohzu SC-800 motor controller setup parameters:
#     (1) maximum number of controllers in system
#     (2) motor task polling rate (min=1Hz,max=60Hz)
SC800Setup(5, 60)
However the max polling rate I see is ~ 22Hz. I am not sure why the motors are not being polled at 60Hz.
camonitor -tIs VPFI:KOHZU:m1.RBV
VPFI:KOHZU:m1.RBV              2016-03-08 17:54:02.824819 -1.5
VPFI:KOHZU:m1.RBV                              +57.093353 -1.48
VPFI:KOHZU:m1.RBV                               +0.043757 -1.46825
VPFI:KOHZU:m1.RBV                               +0.045044 -1.457
VPFI:KOHZU:m1.RBV                               +0.046047 -1.4455
VPFI:KOHZU:m1.RBV                               +0.044958 -1.43425
VPFI:KOHZU:m1.RBV                               +0.045999 -1.42275
VPFI:KOHZU:m1.RBV                               +0.045986 -1.41125
VPFI:KOHZU:m1.RBV                               +0.045030 -1.4025
I have tried removing all but one SC-410 controller, to see if it is because of the GPIB cable. I have also tried just having one SC-410 controller with one axis connected (each controller can supports a max of 4 axes), but I don’t see a change in the polling rate. I also don’t think it is the GPIB controller card, since I have tested two cards (Agilent 82350b and NI PCI-e GPIB) now, and in both cases the max polling rate is see is 20Hz. Also I don’t really see a big difference in the polling rate when the cpu is under high load vs. low load. I am not sure if it is the controller limit at this point (I could not find any documentation regarding how fast the controllers can poll, maybe I need to look harder)  I am using linux-gpib-4.0.2, asyn-4-26, motor-6-9, base-3.14.12.5.
Any help is appreciated on this.
Also some of the stages, we have do not have an origin sensor on the motor shaft, so the origin return sequence 3 for homing the stages no longer works. I temporarily changed it to look for the NORG (origin proximity sensor)
case HOME_FOR:
case HOME_REV:
           rtnval = write_parms(pbuff, signal, cntrl, motor_call, command, mr);
           sprintf(buff, "ORG%d/2/0/0/4/1", axis);
           break;
but then I need to change it back for the one’s that do have an origin sensor. Is there a better way to do this. Maybe have a record for home search?  For the time being i just use HOME_FOR to use method 4 (look for NORG) and then HOM_REV stays as is.
Best,
Ali
Re: Kohzu motors poll rate issue?? Ron Sluiter
Kohzu motors poll rate issue?? Alireza Panna
RE: Kohzu motors poll rate issue?? Mark Rivers
Re: Kohzu motors poll rate issue?? Alireza Panna
Prev: Re: IoC support for Rohde & Schwarz SMA100A Jack
Next: Re: IoC support for Rohde & Schwarz SMA100A Eric Norum
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024
Prev: Re: Kohzu motors poll rate issue?? Alireza Panna
Next: Re: Kohzu motors poll rate issue?? Ron Sluiter
ANJ, 15 Jul 2016 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·
