1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024
Subject: Re: 5 counts in 1 hour
Date: Thu, 7 Jan 2016 17:41:20 -0500
The way a db record interprets the value of a waveform/compress VAL field is not the same as when one performs a caget in a terminal? In a terminal, ( $>> caget somePVwaveform ) returns the entire array of values for the record. When called inside the CALC record, only the first item of the array is returned?
-Tim
On 1/7/16 12:20 PM, Andrew Johnson wrote:
Hi Tim,
On 01/07/2016 10:41 AM, Southern, Tim wrote:
Problem:
We have a spark detector that will increment a counter every time a
spark is detected.  The user requests an alarm when the counter
increments +5 times within an hour. How can this be implemented on an IOC?
Nice little problem.
A Solution:
I came up with a solution using compress records. First, I created
a 3600 element compress record using a circular buffer that records the
value of the PV counter every second for an hour.  Next, I created two
more compress records, one that saved the lowest value, and one that
saved the highest value of the first record (N to 1 Low Value, N to 1
High Value). I then created a CALC record that calculated the difference
of the low and high values. When CALC is greater than 5 ... then alarm.
Is there a better implementation to do this? Is there anything wrong
with this solution?
Assuming that your input is a counter that only ever increments, you
really only need the first compress record and a calc. The output from
your High Value compress will always be the same as the current spark
count $(S):FltCtr, and the first element read from the circular buffer
is the oldest value in the buffer (the one from an hour ago), which is
always the same as the output from your Low Value compress. Thus the
following is equivalent to your solution with fewer records:
# Alarm for greater than 5 counts in 1 hour
# Circular buffer of spark counts
record(compress,"$(S):1HrCmp"){
  field(SCAN, "1 second")
  field(NSAM, "3600")
  field(N, "3600")
  field(ALG, "Circular Buffer")
  field(INP, "$(S):FltCtr")   # ←- Record that increments
# Difference of High and Low over time of circular buffer
# Alarms when count is greater than 5
record(calc, "$(S):1HrCmp_diff"){
  field(INPA, "$(S):1HrCmp CP")
  field(INPB, "$(S):FltCtr")
  field(CALC, "B-A")
  field(HIGH, "5")
  field(HSV, "MAJOR")
HTH,
- Andrew
RE: 5 counts in 1 hour Mark Rivers
Re: 5 counts in 1 hour Andrew Johnson
5 counts in 1 hour Southern, Tim
Prev: RE: areaDetector driver pixel types Mark Rivers
Next: RE: 5 counts in 1 hour Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <20162017  2018  2019  2020  2021  2022  2023  2024
Prev: Re: 5 counts in 1 hour Andrew Johnson
ANJ, 15 Jul 2016 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·
