1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017  2018  2019  2020  2021  2022  2023  2024
Subject: RE: ai RVAL via asyn + modbus: getting unsigned integer
Date: Thu, 3 Dec 2015 18:37:37 +0000
Hi Jon,
I didn't realize you were running an old version of modbus.
In R2-2 this is from the readInt32 function:
            switch(pPlc->modbusFunction) {
                case MODBUS_READ_COILS:
                case MODBUS_READ_DISCRETE_INPUTS:
                case MODBUS_READ_HOLDING_REGISTERS:
                case MODBUS_READ_INPUT_REGISTERS:
                    *value = pPlc->data[offset];
                     break;
pPlc->data is unsigned short, so it will be copied to *value without casting to signed.
In R2-4 and later this is from readInt32:
                case MODBUS_READ_INPUT_REGISTERS_F23:
                    status = readPlcInt(pPlc, offset, value);
                    if (status != asynSuccess) return status;
                    break;
This is from  readPlcInt:
    switch (dataType) {
        case dataTypeUInt16:
            result = value;
            break;
        case dataTypeInt16:
            result = (epicsInt16)value;
            break;
So for data type 4 (dataTypeInt16) it casts the value to epicsInt16 (signed) before copying to the epicsInt32 value.
If you want to correctly handle the data from your device you need to upgrade to modbus R2-4 or later.
Sent: Thursday, December 03, 2015 12:16 PM
To: Mark Rivers
Cc: [email protected]
On Thu, 3 Dec 2015, Mark Rivers wrote:
> Hi Jon,
> http://cars9.uchicago.edu/software/epics/modbusDoc.html
> Supported Modbus data types
> modbusDataType value    drvUser field   Description
> 0       UINT16  Unsigned 16-bit binary integers
> 4       INT16   16-bit signed (2's complement) integers. This data type extends the sign bit when converting to epicsInt32.
> So modbusDataType=0 is UINT16, unsigned 16-bit integer.  That explains your problem, you should be using modbusDataType=4 (INT16) and your command line should be:
> drvModbusAsynConfigure("CollimCouch", "AcromagCollimCouch",0,4,0,9,4,100,"AcromagXT1221")
That must be it.  The referenced documentation is for Modbus release 2-7 and
we are still running 2-2, which only supports data type codes 0 - 3.  When we try
code 4 in 2-2, RVAL is always 0.  The 2-2 doc says:
Type 0 is used for binary numbers in twos-complement format. The data can either be signed or unsigned.
But, as we found, it isn't very helpful for signed integers.
Thanks for clearing this up.
Jon Jacky
RE: ai RVAL via asyn + modbus: getting unsigned integer Mark Rivers
RE: ai RVAL via asyn + modbus: getting unsigned integer jon
Prev: RE: ai RVAL via asyn + modbus: getting unsigned integer jon
Next: EPICS 2016 Spring Meeting at ESS, Lund, Sweden Timo Korhonen
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017  2018  2019  2020  2021  2022  2023  2024
Next: RE: ai RVAL via asyn + modbus: getting unsigned integer jon
ANJ, 16 Dec 2015 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·