Argonne National Laboratory
1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017
Subject: Re: Modbus Binary Output Readbacks
To: Mark Rivers <rivers@cars.uchicago.edu>
Cc: "Wallace, Alex" <awallace@slac.stanford.edu>, "tech-talk@aps.anl.gov" <tech-talk@aps.anl.gov>
Date: Wed, 14 Oct 2015 21:29:45 -0500
I read this as a request for the modbus record to internally do this, so that you don't have to set up one block of registers to read, and then a different set with a different name to write.  No?
On Oct 14, 2015, at 21:21, Mark Rivers <rivers@cars.uchicago.edu> wrote:
Hi Alex,
You can definitely have 2 two modbus ports pointing at the same registers, one for read and write.
One way to keep your bo record in sync with the coil is to use the following database construct.
record(bo, "$(P)$(R)B0")
   field(OUT, "$(P)$(R)BO_write PP")
record(bo, "$(P)$(R)B0_write")
   field(SDIS, "$(P)$(R)B0_Sync.PACT")
   field(DISV, "1")
   field(DTYP, "asynInt32")
   field(OUT, "@asyn($(OUTPORT),$(ADDR),$(TIMEOUT))")
record(bi, "$(P)$(R)BI")
   field(INP,  "@asyn($(INPORT),$(ADDR),$(TIMEOUT))")
   field(SCAN, "I/O Intr")
   field(FLNK, "$(P)$(R)B0_Sync")
record(bo, "$(P)$(R)BO_Sync")
   field(DOL,  "$(P)$(R)BI NPP")
   field(OMSL, "closed_loop")
   field(OUT,  "$(P)$(R)BO PP")
The BO record is the record your application writes to.  It uses soft device support.  It sends its output to the BO_write record that actually does the modbus write.  That record is disabled if it is being processed as a result of a callback to the bi record.  The BI record is I/O Intr processed when the coil value changes.  It writes the value to the BO record via the BO_sync record.  Note that I took this example from a non-modbus application so the DTYP and asyn link syntax is probably wrong, but you get the idea.
From: tech-talk-bounces@aps.anl.gov [tech-talk-bounces@aps.anl.gov] on behalf of Wallace, Alex [awallace@slac.stanford.edu]
Sent: Wednesday, October 14, 2015 8:51 PM
To: tech-talk@aps.anl.gov
Subject: Modbus Binary Output Readbacks
Can anyone see an issue with modifying the modbus module to give certain records, eg. binary output (bo), two modbus ports to use, one for writes and one to keep the record syncd with the PLC output coil state?
There should be no reason I can see for having two modbus ports pointing at the same registers, one for read and write. But as for the bo record, I'm not really sure where to begin.
Thanks!
-Alex
RE: Modbus Binary Output Readbacks Mark Rivers
Modbus Binary Output Readbacks Wallace, Alex
Prev: RE: Modbus Binary Output Readbacks Mark Rivers
Next: RE: Modbus Binary Output Readbacks Mark Rivers
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <20152016  2017
ANJ, 16 Dec 2015 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·