Hello Tobin,
First, I think you may be mixing your protocol layers. The only
"PSH" I see in your packet dump is the TCP flag, which is a hint
to the receiver's IP stack to deliver data to the user
application. Unless Acromag is using a custom IP stack this is
probably of no consequence. The exception are modbus/tcp errors,
in this case indicating that an illegal function code (1) is being
used. Most modbus devices implement only a few of the defined
function codes (aka types of operations).
Looking at your packet capture I see several strange things.
1) The duplicate acks with 300ms delay are an indication of packet
loss incurring a TCP retransmit.
2) The host .182 is sending a truncated/invalid request of only 6
bytes (or wireshark is dropping packets).
I'm guessing this has something to do with a missing
drvModbusAsynConfigure() iocsh command, which is how the modbus
driver is instructed as to which function code to use.
An example using a modbus RTU serial device.
drvAsynSerialPortConfigure("A",
"/dev/ttyACM0", 0, 0, 0)
asynSetOption("A",0,"baud","115200")
modbusInterposeConfig("A", 1)
# PORT, SRC, SADDR, FUNC, OFFSET, LEN, TYPE, POLL, ID
drvModbusAsynConfigure("AREAD", "A", 0, 3, 0, 8, 0, 1000,
"ARDR")
drvModbusAsynConfigure("AWRITE","A", 0, 6, 0, 8, 0, 1000,
"ARDW")
dbLoadRecords("../../db/asynRecord.db","P=test:,R=portr,PORT=AREAD,ADDR=0,IMAX=40,OMAX=40")
dbLoadRecords("../../db/asynRecord.db","P=test:,R=portw,PORT=AWRITE,ADDR=1,IMAX=40,OMAX=40")
Defines asyn ports "AREAD" and "AWRITE" which use function codes 3
and 6 respectively. See the modbus driver documentation for the
meaning of the other arguments.
Michael
On 09/05/2014 06:11 PM, Tobin Weber wrote:
Hello Colleagues,
We use a type of distributed I/O device that talks Modbus
TCP/IP called an Acromag 952EN-4012. We have had re-occurring
issues with these devices over the last few years. Most
recently, we have experienced the devices losing communication
with our EPICS IOC. We believe we have traced the source of this
problem down to a Port checking procedure that we were doing.
This procedure simply involves processing an asyn record that is
linked to the IP Port created for modbus access.
The simplest example of an IOC that produces these errors is
created with the following start up file:
drvAsynIPPortConfigure("ReadPort","192.168.0.78:502",0,0,1)
modbusInterposeConfig("ReadPort", 0, 1000,0)
dbLoadRecords("db/PortCheck.vdb")
With PortCheck.vdb being:
record(asyn, AcroRead) {
field(PORT, "ReadPort")
field(TMOD, "Write/Read")
field(SCAN, "1 second")
We usually read the .ERRS and .CNCT fields on AcroRead to
check the port, but I left that out of the epics code b/c it
doesn't appears to make a difference.
When AcroRead processes, we think the CPU (0.182) sends a
"PSH" or Push Command to the Acromag Device (0.78) [See attached
wirehshark file Acroamg_Port_Check_Tech_Talk]. After
acknowledging this packet, the Acromag device responds with an
exception. It appears to not understand the "PSH" command. I've
spoken with Acromag Engineers and they said their devices will
not know how to process this command.
We are fairly certain that this process, when combined with
the reads and writes we do, will intermittently cause the
Acromag device to stop responding completely to the EPICS IOC.
My question: Is the "PSH" command being sent expected behavior
in this situation? What are the origins of this command?
Thanks very much for any help you can provide.
Toby
Tobin Weber
University of Washington
Fast Neutron Therapy
206-598-0485