1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <20142015  2016  2017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <20142015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Subject: RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
To: Dirk Zimoch <[email protected]>, "[email protected]" <[email protected]>, "[email protected]" <[email protected]>
Date: Fri, 11 Apr 2014 11:11:12 +0000
Eric reproduced the problem yesterday, and we think we understand the problem.  It appears to actually be a problem with asyn, not with StreamDevice.
The problem does not occur for normal read operationgs with a non-zero timeout.  In that case if read() returns an error indicating that the device is no longer available then the driver disconnects the port.  For the next read or write operation asynManager will see that the port is disconnected, and will try the normal autoconnect mechanism. When the device available again it will connect.
The problem is occurring when StreamDevice calls read with a zero timeout, which it does to simulate a flush() operation.  In this case the driver is calling fcntl() which is returning an error.  It then returns that error to StreamDevice.  But it does not disconnect the port when this occurs, like it does when a read() error occurs.  It should be disconnecting the port.  There may be a few other places where errors should cause the port to disconnect.
As a side note, why is StreamDevice calling read() with zero timeout, rather than calling flush()?
I think the fix should be pretty easy.  I will try to reproduce the problem today, and then verify that it is fixed.
From: [email protected] [[email protected]] on behalf of Dirk Zimoch [[email protected]]
Sent: Friday, April 11, 2014 2:22 AM
To: [email protected]
Subject: Re: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
Hi Tomáš,
I will have a look. In older versions of StreamDevice, I check the
connection state at each access and try to connect if necessary. But I
have been told that this is wrong behavior and I should better leave it
to asyn to do the auto connect. So I removed the connect code from
StreamDevice. This worked fine with sockets. But I have to investigate
what is missing with USB to serial. I also check with Mark and Eric. But
it may take a while...
Dirk
On 10.04.2014 13:24, Mazanec Tomáš wrote:
> In synApps 5.7, if the usb-serial device is physically disconnected,
> while the IOC is running, the command:
> asynReport(10, PORT) says the asyn port is still connected:
> PORT multiDevice:No canBlock:Yes autoConnect:Yes
>      enabled:Yes connected:Yes numberConnects 1
>      nDevices 0 nQueued 0 blocked:No
>      asynManagerLock:No synchronousLock:Yes
>      exceptionActive:No exceptionUsers 2 exceptionNotifys 0
>      interposeInterfaceList
>          asynOctet pinterface 0x7fbbfb51f6a0 drvPvt 0x1489670
>      interfaceList
>          asynCommon pinterface 0x7fbbfb51ca80 drvPvt 0x1486740
>          asynOption pinterface 0x7fbbfb51caa0 drvPvt 0x1486740
>          asynOctet pinterface 0x7fbbfb51ee40 drvPvt 0x1486740
> Serial line /dev/ttyUSBPIC: Connected
>                      fd: 5
>      Characters written: 164
>         Characters read: 287
> What also happens, and I didn't noticed, is IOC's process takes 100% CPU
> usage and traceFlow bit within traceMask in Asyn reports hundreds of
> these lines in a second:
> 2014/04/10 13:06:39.575 /dev/ttyUSBPIC read.
> However, an attempt to reconnect asyn port with asynRecord ends with no
> success and this messsage output:
> 2014/04/10 13:04:32.374 EEE:asynrec: special queueRequest timeout
> Thanks,
> Tomas
> *Od:* Mark Rivers [[email protected]]
> *Odesláno:* 8. dubna 2014 18:47
> *Komu:* Mazanec Tomáš; [email protected]
> *Předmět:* RE: Streamdevice 2.6 autoconnection failure using
> drvAsynSerialPort
> In synApps 5.7 what happens if you use an asynRecord to force the
> asynPort to reconnect.  Does StreamDevice then start working?
> When the device is disconnected does asyn report that it is
> disconnected?  Use the following command when the device is disconnected:
> asynReport 10 ASYN_PORT_NAME
> Mark
> *From:*Mazanec Tomáš [mailto:[email protected]]
> *Sent:* Tuesday, April 08, 2014 9:20 AM
> *To:* Mark Rivers; [email protected]
> *Subject:* RE: Streamdevice 2.6 autoconnection failure using
> drvAsynSerialPort
> Hi Mark
> Thanks for a quick response.
> The IOC runs on Scientific Linux 6.5 x86-64 and its default kernel.
> Yes, I have upgraded it (from 6.4 to 6.5) prior to SynApps upgrade.
> Linux udev system is configured in a way that my usb-serial device gets
> always the same device name (/dev/ttyUSBPIC) no matter what other
> devices are present (major, minor device numbers can change).
> I've double-checked Asyn 4.21 re-connection ability using asynRecord
> (.CNCT, .PCNCT).
> It works fine, so the issue might be a glitch in the new StreamDevice.
> Nevertheless, I've kept SynApps-5-6 installed and compared re-connection
> behavior to 5.7.
> The older version is fine -- If my usb-serial device is physically
> disconnected, IOC with SynApps-5-6 reports:
> 2014/04/07 16:55:20.994 PORT EEE:volts: connection closed in write
> 2014/04/07 16:55:25.994 PORT EEE:volts: pasynCommon->connect() failed:
> /dev/ttyUSBPIC Can't open  No such device
> 2014/04/07 16:55:25.994 PORT EEE:volts: Protocol aborted
> and when the usb-serial device is connected back, R/W operations
> continue as usual.
> Whereas with the new version (5.7), IOC shell is kind of silent unless I
> try to reload StreamDevice protocol :
> epics> streamReload EEE:volts
> 2014/04/08 11:46:52.567355 _main_ StreamCore::finishProtocol(EEE:volts):
> Still waiting for writeSuccess()
> 2014/04/08 11:46:52.567398 _main_ EEE:volts: Protocol aborted
> or unless I try to use StreamDevice's connect command (through the
> EEE:CONNECT PV):
> epics> dbpf EEE:CONNECT 1
> DBR_STRING:          "ON"
> epics> 2014/04/07 17:10:06.446437 timerQueue EEE:CONNECT: Connect failed
> 2014/04/07 17:10:06.446482 timerQueue EEE:CONNECT: Protocol aborted
> ?2014/04/07 17:10:07.536724 timerQueue EEE:CONNECT: Connect failed
> ?2014/04/07 17:10:07.536747 timerQueue EEE:CONNECT: Protocol aborted
> but the connection is not re-established anyway. Furthermore, protocol
> reload makes IOC shell stuck.
> There is an older post about different connection issue, but also with
> StreamDevice & Asyn.
> So, with the new version (5.7), I've checked whether the timerQueue
> thread is OK and checked for any locked mutexes.
> The thread is OK.
> There is a mutex reported as locked once the usb-serial device is
> diconnected, however it remains locked when the device is connected back.
> epics> epicsMutexShowAll 1
> ellCount(&mutexList) 112 ellCount(&freeList) 0
> epicsMutexId 0x1d5bfd0 source ../../asyn/asynDriver/asynManager.c line 1868
> No mutexes remain locked after the usb-device re-connection with the
> older version (5.6). But this could be just a result of the issue.
> Tomas
> *Od:*Mark Rivers [[email protected]]
> *Odesláno:* 7. dubna 2014 18:36
> *Komu:* Mazanec Tomáš; [email protected] <mailto:[email protected]>
> drvAsynSerialPort
> Hi Tomas,
> There were no substantive changes in the drvAsynSerialPort code between
> asyn 4.18 and asyn 4.21.  SVN tag 1917 is asyn 4.18 and tag 2203 is asyn
> 4.21.
> Here are the differences:
> corvette:asyn/asyn/drvAsynSerial>svn diff -r1917:2203 drvAsynSerialPort*
> Index: drvAsynSerialPort.c
> --- drvAsynSerialPort.c (revision 1917)
> +++ drvAsynSerialPort.c (revision 2203)
> @@ -103,12 +103,12 @@
>       if ((ioctl(tty->fd, FIOBAUDRATE, tty->baud) < 0)
>        && (ioctl(tty->fd, SIO_BAUD_SET, tty->baud) < 0)) {
>           epicsSnprintf(pasynUser->errorMessage,
> pasynUser->errorMessageSize,
> -                                "SIO_BAUD_SET failed: %s\n",
> strerror(errno));
> +                                "SIO_BAUD_SET failed: %s",
> strerror(errno));
>           return asynError;
>       if (ioctl(tty->fd, SIO_HW_OPTS_SET, tty->termios.c_cflag) < 0) {
> -                               "SIO_HW_OPTS_SET failed: %s\n",
> strerror(errno));
> +                               "SIO_HW_OPTS_SET failed: %s",
> strerror(errno));
>           return asynError;
> #else
> @@ -116,7 +116,7 @@
>       tty->termios.c_cflag |= CREAD;
>       if (tcsetattr(tty->fd, TCSANOW, &tty->termios) < 0) {
> -                                   "tcsetattr failed: %s\n",
> strerror(errno));
> +                                   "tcsetattr failed: %s",
> strerror(errno));
>           return asynError;
> #endif
> @@ -253,12 +253,12 @@
>           if(cfsetispeed(&tty->termios,baudCode) < 0 ) {
> epicsSnprintf(pasynUser->errorMessage,pasynUser->errorMessageSize,
> -                "cfsetispeed returned %s\n",strerror(errno));
> +                "cfsetispeed returned %s",strerror(errno));
>               return asynError;
>           if(cfsetospeed(&tty->termios,baudCode) < 0 ) {
> -                "cfsetospeed returned %s\n",strerror(errno));
> +                "cfsetospeed returned %s",strerror(errno));
>               return asynError;
> @@ -452,7 +452,7 @@
>       tcflush(tty->fd, TCOFLUSH);
> #endif
> #ifdef vxWorks
> -    ioctl(tty->fd, FIOCANCEL, NULL);
> +    ioctl(tty->fd, FIOCANCEL, 0);
>        * Since it is possible, though unlikely, that we got here before the
>        * slow system call actually started, we arrange to poke the thread
> @@ -509,14 +509,14 @@
>       if ((tty->fd = open(tty->serialDeviceName,
> O_RDWR|O_NOCTTY|O_NONBLOCK, 0)) < 0) {
> -                            "%s Can't open  %s\n",
> +                            "%s Can't open  %s",
> strerror(errno));
>           return asynError;
> #if defined(FD_CLOEXEC) && !defined(vxWorks)
>       if (fcntl(tty->fd, F_SETFD, FD_CLOEXEC) < 0) {
> -                            "Can't set %s close-on-exec flag: %s\n",
> +                            "Can't set %s close-on-exec flag: %s",
> strerror(errno));
>           close(tty->fd);
>           tty->fd = -1;
> @@ -578,7 +578,7 @@
>       asynPrint(pasynUser, ASYN_TRACE_FLOW,
>                               "%s write.\n", tty->serialDeviceName);
>       asynPrintIO(pasynUser, ASYN_TRACEIO_DRIVER, data, numchars,
> -                            "%s write %d\n", tty->serialDeviceName,
> numchars);
> +                            "%s write %lu\n", tty->serialDeviceName,
> (unsigned long)numchars);
>       if (tty->fd < 0) {
>                                   "%s disconnected:",
> @@ -672,7 +672,7 @@
>       if (maxchars <= 0) {
> -            "%s maxchars %d Why
> <=0?\n",tty->serialDeviceName,(int)maxchars);
> +            "%s maxchars %d Why <=0?",tty->serialDeviceName,(int)maxchars);
>           return asynError;
>       if (tty->readTimeout != pasynUser->timeout) {
> @@ -775,8 +775,8 @@
>          data[nRead] = 0;
>       else if (gotEom)
>           *gotEom = ASYN_EOM_CNT;
> -    asynPrint(pasynUser, ASYN_TRACE_FLOW, "%s read %d, return %d\n",
> -                            tty->serialDeviceName, *nbytesTransfered,
> status);
> +    asynPrint(pasynUser, ASYN_TRACE_FLOW, "%s read %lu, return %d\n",
> +                            tty->serialDeviceName, (unsigned
> long)*nbytesTransfered, status);
>       return status;
> So the changes are removing “\n” from the end of epicsSNprintf formats,
> and some other minor changes to avoid compiler warnings.
> Is this on Linux?
> Have you upgraded the OS?
> I think any change in behavior is likely due either to a change in
> StreamDevice or a change in the OS, and not due to any change in asyn.
> Mark
> *From:*[email protected]
> [mailto:[email protected]] *On Behalf Of *Mazanec Tomáš
> *Sent:* Monday, April 07, 2014 11:13 AM
> *To:* [email protected] <mailto:[email protected]>
> *Subject:* Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
> Hello
> Automatic re-connection seems to be broken with recent streamdevice & asyn.
> Recently, we upgraded SynApps from 5.6 to version 5.7 and so
> streamdevice 2.5.1 & Asyn 4.18 to streamdevice 2.6 & Asyn 4.21.
> One of IOCs here is using serial port ( as /dev/ttyUSBxxx ) and device
> controlled by it disconnects often.
> With SynApps 5.6, everything ran smoothly. After the upgrade to SynApps
> 5.7, the IOC is not able to reconnect anymore.
> As far as I've tested, drvAsynIPPort reconnects well with both SynApps
> 5.6 and 5.7, so its just serial port variant which is affected.
> Could you anyone address this issue and provide some hints or fix.
> Regards,
> Tomas Mazanec
> ELI Beamlines Czech Republic
> http://www.eli-beams.eu
> +420 26605 2566
> +420 601 555 066
> Address:
> Institute of Physics, Academy of Sciences
> Na Slovance 2
> 182 21 Prague
> Czech Republic
> *** DB template file:
> record(ai, "$(NAME):volts")
>      field(DTYP, "stream")
>      field(INP, "@$(SCONF) get_volts $(ASYNPORT)")
>      field(SCAN, "5 second")
>      field(PINI, "YES")
>      field(VAL, "0")
>      field(PREC, "2")
>      field(EGU, "V")
> record(bo, "$(NAME):CONNECT") {
>    field(OUT, "@$(SCONF) connect $(ASYNPORT)")
>    field(PINI, "NO")
>    field(HIGH, "0.1")
>    field(ZNAM, "OFF")
>    field(ONAM, "ON")
> *** streamdev protocol file:
> get_volts    {out "\x11\x3f\x76\x04"; in "\x76%f\x04\x00" }
> connect {
>      ExtraInput = Ignore;
>      connect 1000;
> *** EPICS IOC shell LOG file:
> epicsEnvSet("SYSNAME","EEE")
> # streamdevice protocol file-name
> epicsEnvSet("SYSSCONF","proto.sdp")
> # name of asyndriver port (arbitrary)
> epicsEnvSet("SYSASYNPORT","PORT")
> # For streamdevice
> epicsEnvSet STREAM_PROTOCOL_PATH :protocols:./cfg
> # Setup asyn driver
> drvAsynSerialPortConfigure ("PORT","/dev/ttyUSBPIC", 0, 1, 0)
> asynSetOption ("PORT", 0, "baud", "9600")
> asynSetOption ("PORT", 0, "bits", "8")
> asynSetOption ("PORT", 0, "parity", "none")
> asynSetOption ("PORT", 0, "stop", "1")
> asynReport(1, "PORT")
> PORT multiDevice:No canBlock:Yes autoConnect:No
>      enabled:Yes connected:No numberConnects 0
>      asynManagerLock:No synchronousLock:No
>      exceptionActive:No exceptionUsers 1 exceptionNotifys 0
> Serial line /dev/ttyUSBPIC: Disconnected
>                      fd: -1
>      Characters written: 0
>         Characters read: 0
> asynSetTraceIOMask("PORT",0,0x4)
> asynSetTraceMask("PORT",0,0x9)
> dbLoadRecords("aaa.template","NAME=EEE, SCONF=proto.sdp, ASYNPORT=PORT")
> iocInit()
> Starting iocInit
> ## EPICS R3.14.12.4 $Date: Mon 2013-12-16 15:51:45 -0600$
> ## EPICS Base built Mar 11 2014
> iocRun: All initialization complete
> 2014/04/07 17:07:24.528 /dev/ttyUSBPIC write 4
> 11 3f 76 04
> 2014/04/07 17:07:24.542 /dev/ttyUSBPIC read 1
> 76
> 2014/04/07 17:07:24.543 /dev/ttyUSBPIC read 1
> 35
> 2014/04/07 17:07:24.544 /dev/ttyUSBPIC read 1
> 2e
> 2014/04/07 17:07:24.545 /dev/ttyUSBPIC read 1
> 31
> 2014/04/07 17:07:24.547 /dev/ttyUSBPIC read 1
> 39
> 2014/04/07 17:07:24.548 /dev/ttyUSBPIC read 1
> 04
> 2014/04/07 17:07:24.549 /dev/ttyUSBPIC read 1
> 00
> 2014/04/07 17:07:29.026 /dev/ttyUSBPIC write 4
> 11 3f 76 04
> 2014/04/07 17:07:29.039 /dev/ttyUSBPIC read 1
> 76
> 2014/04/07 17:07:29.041 /dev/ttyUSBPIC read 2
> 35 2e
> 2014/04/07 17:07:29.042 /dev/ttyUSBPIC read 1
> 31
> 2014/04/07 17:07:29.043 /dev/ttyUSBPIC read 1
> 39
> 2014/04/07 17:07:29.044 /dev/ttyUSBPIC read 1
> 04
> 2014/04/07 17:07:29.046 /dev/ttyUSBPIC read 1
> 00
> epics>
> epics>
> epics>
> epics> scanppl
> Records with SCAN = '5 second' (0 over-runs):
>      EEE:volts
> epics> dbgf EEE:volts
> DBR_DOUBLE:         5.19
> epics>
> epics> dbpr EEE:volts 111
> ACKS: INVALID       ACKT: YES           ADEL: 0             ALST: 5.19
> AOFF: 0             ASG:                ASLO: 1             ASP: (nil)
> BKPT: 00            DESC:               DISA: 0             DISP: 0
> DISS: NO_ALARM      DISV: 1             DPVT: 0x1911dd0     DSET:
> 0x7fa011b09a40
> DTYP: stream        EGU: V              EGUF: 0             EGUL: 0
> EOFF: 0             ESLO: 1             EVNT: 0             FLNK:CONSTANT 0
> HHSV: NO_ALARM      HIGH: 0             HIHI: 0             HOPR: 0
> HSV: NO_ALARM       HYST: 0             INIT: 0
> INP:INST_IO @proto.sdp get_volts PORT   LALM: 5.19          LBRK: 0
> LCNT: 11            LINR: NO CONVERSION LLSV: NO_ALARM      LOLO: 0
> LOPR: 0             LOW: 0              LSET: 0x1917c90     LSV: NO_ALARM
> MDEL: 0
> MLIS: 30 69 02 b0 9f 7f 00 00 30 69 02 b0 9f 7f 00 00 01 00 00 00
> MLOK: 40 76 90 01 00 00 00 00           MLST: 5.19          NAME: EEE:volts
> NSEV: NO_ALARM      NSTA: NO_ALARM      ORAW: 0             PACT: 1
> PBRK: (nil)         PHAS: 0             PINI: YES           PPN: (nil)
> PPNR: (nil)         PREC: 2             PRIO: LOW           PROC: 0
> PUTF: 0             RDES: 0x1885ff0     ROFF: 0             RPRO: 0
> RSET: 0x7fa0118c7a80                    RVAL: 0             SCAN: 5 second
> SDIS:CONSTANT       SEVR: INVALID       SIML:CONSTANT       SIMM: NO
> SIMS: NO_ALARM      SIOL:CONSTANT       SMOO: 0             SPVT: 0x1913f00
> STAT: SCAN          SVAL: 0             TIME: 2014-04-07 17:07:34.247219579
> TPRO: 0             TSE: 0              TSEL:CONSTANT       UDF: 0
> VAL: 5.19
> epics>
> epics> dbgf EEE:volts.SEVR
> DBR_STRING:          "INVALID"
> epics>
> DBR_STRING:          "ON"
> epics> ?[31;1m2014/04/07 17:10:06.446437 timerQueue EEE:CONNECT: Connect
> failed
> ?[0m?[31;1m2014/04/07 17:10:06.446482 timerQueue EEE:CONNECT: Protocol
> aborted
> ?[0m?[31;1m2014/04/07 17:10:07.536724 timerQueue EEE:CONNECT: Connect
> failed
> ?[0m?[31;1m2014/04/07 17:10:07.536747 timerQueue EEE:CONNECT: Protocol
> aborted
> ?[0m
> epics>
> epics> var streamDebug 1
> 2014/04/07 17:10:35.596373 _main_ StreamEpics.cc:711:
> Stream::process(EEE:CONNECT) start
> 2014/04/07 17:10:35.596411 _main_ StreamCore.cc:410:
> StreamCore::startProtocol(EEE:CONNECT, startMode=StartNormal)
> 2014/04/07 17:10:35.596426 _main_ StreamCore.cc:552:
> StreamCore::evalCommand(EEE:CONNECT): activeCommand = connect
> 2014/04/07 17:10:35.596436 _main_ AsynDriverInterface.cc:1347:
> AsynDriverInterface::connectRequest EEE:CONNECT
> 2014/04/07 17:10:35.596446 _main_ StreamEpics.cc:723:
> Stream::process(EEE:CONNECT): protocol started
> DBR_STRING:          "ON"
> epics> 2014/04/07 17:10:36.591508 timerQueue
> AsynDriverInterface.cc:1473:
> AsynDriverInterface::handleTimeout(EEE:CONNECT)
> ?[31;1m2014/04/07 17:10:36.591531 timerQueue EEE:CONNECT: Connect failed
> ?[0m2014/04/07 17:10:36.591539 timerQueue StreamCore.cc:517:
> StreamCore::finishProtocol(EEE:CONNECT, status=Fault) not bus owner
> 2014/04/07 17:10:36.591545 timerQueue AsynDriverInterface.cc:1416:
> AsynDriverInterface::finish(EEE:CONNECT) start
> 2014/04/07 17:10:36.591551 timerQueue AsynDriverInterface.cc:1426:
> AsynDriverInterface::finish(EEE:CONNECT) done
> ?[31;1m2014/04/07 17:10:36.591557 timerQueue EEE:CONNECT: Protocol aborted
> ?[0m2014/04/07 17:10:36.591589 cbLow StreamEpics.cc:896:
> streamRecordProcessCallback(EEE:CONNECT) processing record
> 2014/04/07 17:10:36.591622 cbLow StreamEpics.cc:691:
> Stream::process(EEE:CONNECT) error status=UDF (17)
> 2014/04/07 17:10:36.591646 cbLow StreamEpics.cc:901:
> streamRecordProcessCallback(EEE:CONNECT) processing record done
> 2014/04/07 17:10:36.686741 cbLow StreamEpics.cc:711:
> 2014/04/07 17:10:36.686766 cbLow StreamCore.cc:410:
> 2014/04/07 17:10:36.686779 cbLow StreamCore.cc:552:
> 2014/04/07 17:10:36.686785 cbLow AsynDriverInterface.cc:1347:
> 2014/04/07 17:10:36.686796 cbLow StreamEpics.cc:723:
> 2014/04/07 17:10:37.681881 timerQueue AsynDriverInterface.cc:1473:
> ?[31;1m2014/04/07 17:10:37.681901 timerQueue EEE:CONNECT: Connect failed
> ?[0m2014/04/07 17:10:37.681909 timerQueue StreamCore.cc:517:
> 2014/04/07 17:10:37.681916 timerQueue AsynDriverInterface.cc:1416:
> 2014/04/07 17:10:37.681922 timerQueue AsynDriverInterface.cc:1426:
> ?[31;1m2014/04/07 17:10:37.681927 timerQueue EEE:CONNECT: Protocol aborted
> ?[0m2014/04/07 17:10:37.681958 cbLow StreamEpics.cc:896:
> 2014/04/07 17:10:37.681981 cbLow StreamEpics.cc:691:
> 2014/04/07 17:10:37.681994 cbLow StreamEpics.cc:901:
> epics>
> epics>
> epics>
RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mark Rivers
Re: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Dirk Zimoch
Prev: RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
Next: RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  <20142015  2016  2017  2018  2019  2020  2021  2022  2023  2024
ANJ, 17 Dec 2015 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·