Eric Rod (APS) discovered last week that his two, rather new, OMS MAXv
boards were not responding to travel limits. OMS has confirmed that in
two versions of the MAXv firmware; 1.41 and 1.42, the default mode of
the limit switches after either a power-up or a reset is, off. In other
words, MAXv's with firmware versions 1.41 or 1.42 will, by default, not
stop moving a motor when a limit switch is activated.
You can determine the firmware version of your OMS MAXv's from the EPICS
iocsh by entering the command; dbior drvMAXv.
If you have MAXv's with firmware versions 1.41 or 1.42 you should
upgrade the firmware (MAXv's are field upgradable) as soon as possible.
Until then you should immediately change the MAXv initialization string
that is passed by the MAXvConfig() command by adding the Limit Mode
command "AA; LM,H,,H;". For example, change this string,
config0="AX LTL PSO; AY LTL PSO; AZ LTL PSO; AT LTL PSO; AU LTH PSO; AV
LTH PSO; AR LTH PSO; AS LTH PSO;"
to this,
config0="AA; LM,H,,H; AX LTL PSO; AY LTL PSO; AZ LTL PSO; AT LTL PSO; AU
LTH PSO; AV LTH PSO; AR LTH PSO; AS LTH PSO;"
Then reboot your system. The limit switches will now be configured for
"the Hard Limit mode, which causes the affected axis or axes to abruptly
halt when a limit condition is encountered."
Ron