1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Subject: RE: Question about epid record
To: "'Bruce Hill'" <[email protected]>
Date: Wed, 27 Feb 2013 15:37:58 +0000
Hi Bruce,
I think I see a source of confusion.  These are the comments from devEpidSoft.c
/* A discrete form of the PID algorithm is as follows
 * M(n) = KP*(E(n) + KI*SUMi(E(i)*dT(i))
 *         + KD*(E(n) -E(n-1))/dT(n)
 * where
 *  M(n)    Value of manipulated variable at nth sampling instant
 *  KP,KI,KD Proportional, Integral, and Differential Gains
 *      NOTE: KI is inverse of normal definition of KI
 *  E(n)    Error at nth sampling instant
 *  SUMi    Sum from i=0 to i=n
 *  dT(n)   Time difference between n-1 and n
Note that there is an unmatched open parenthesis in the equation!  It is this one: KP*(
The correct version of that comment, which reflects how the calculation is actually done is:
 *         + KD*(E(n) -E(n-1)))/dT(n)
I added a close parenthesis here: "E(n-1)))/"
So KP is multiplying the entire numerator of that expression, i.e. it multiplies KI and KD.
Both equations in your original message also have that unmatched open parenthesis.
I have fixed the incorrect comment in devEpicsSoft.c and committed to SVN.
Sent: Wednesday, February 27, 2013 12:37 AM
To: Mark Rivers
Cc: [email protected]
Subject: Question about epid record
Hi Mark,
I'm in the process of replacing a genSub based PID controller with
the epid record that you and Bob developed, and I'm puzzled by a difference
in how the two compute the I and D terms.
In the classical PID algorithm, the value of M(n), the manipulated variable is
M(n) = KP*(E(n) + KI*SUMi(E(i)*dT(i)) + KD*(E(n) -E(n-1))/dT(n)
In fact, the above is from line 33 of devEpidSoft.c, and agrees with
other descriptions I've found of the PID calculation.
However, in the do_pid() function, and in epidRecord.html, the
calculation includes the KP gain in the integral and derivative terms.
M(n) = KP*(E(n) + KP*KI*SUMi(E(i)*dT(i)) + KP*KD*(E(n) -E(n-1))/dT(n)
I can scale my KI and KD gain factors by KP to get the equivalent result,
but I don't see why the effective integral gain should be affected when
the proportional gain is tweaked.  Ditto for KD.
Any comments or clarification would be appreciated.
- Bruce
Bruce Hill
Member Technical Staff
SLAC National Accelerator Laboratory
Question about epid record Bruce Hill
Prev: AW: Question about epid record Pal Trivan
Next: Re: Installing EPICS&MEDM on UBUNTU John Hammonds
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  <20132014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Prev: Re: Question about epid record Bruce Hill
Next: 'APS event receiver' type event record can not be processed Zhang Yuliang
ANJ, 20 Apr 2015 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·
