Hi Judy,
Rock, Judith E. wrote:
Hi -
We have a device that returns multiple lines of input from one command. We're successfully using streamdevice to capture the inputs, which are of mixed type. The issue at hand is error handling for the float inputs. Upon error, any of the float fields can return an error string. I tried setting up an @mismatch for the prototype, and this works...the problem is that the prototype stops processing inputs at the error: subsequent inputs in the list are all invalid which could mask some important conditions. I also tried a separate prototype for each input with its own @mismatch; however I observed the same behavior: inputs following the error condition were all invalid.
This is indeed a problem yet unsolved with redirection. The protocol
stops upon error and only the active record becomes invalid.
Our solution at the moment is to read everything in as strings and use scalcouts to translate to numbers - that way each input is converted independently. However, if streamdevice itself has a more elegant way of handling the situation we would be very happy to adopt it!
I can offer you two other solutions:
1) Use "I/O Intr". Like before, you have one active record. But you
don't redirect other values, you simply ignore them. The other records
are "I/O Intr". Their protocol consists only of an 'in' command and they
parse their input and ignore everything else. So if you have a format
like "%*s %*s %f %*s %*s" i.e. read the 3rd of 5 words as a float and
you get an error message as word 3 then this record will simply ignore
the input. If the error strings are enums (i.e. limited set of strings),
you can have the error record for this value trying to read the message
in parallel to the "normal" float input: "%*s %*s
%{error1|error2|error3} %*s %*s".
2) Use a new feature: optional input. With a format like "%?f" you can
read a float or get 0.0 if there is no float.
Something like this:
in "%?f%(e1)?{error1|error2|error3} "
"%(v2)?f%(e2)?{error1|error2|error3}";
If you can give me some example input, I may give you a more detailed
answer.
Drik