Paul:
That's not the device you want. It has 8 DC inputs (DC inputs read from
switches and the like - consider these as boolean signals only). You
want a DC voltage input channel ("AD" in AutomationDirect's terms). The
ethernet support card is correct.
The following card would provide the correct input you need:
F0-04AD-2
4-channel analog input module
12-bit resolution
range: 0-5V or 0-10V
BUT, it takes the one expansion slot available in the D0-05DR PLC.
which means you can't use the H0-ECOM100 module also. Can you do Modbus
over the one of the two serial ports on the D0-05DR?
If not, move to the DL06-series and pick your expansion modules again.
Pete
On 9/27/2011 11:03 AM, Paul Nord wrote:
Mark,
So the entry-level system might look like this:
D0-05DR 8 DC IN / 6 RELAY OUT MICRO PLC W/AC P/S $119.00
H0-ECOM100 10/100MBIT ETHERNET COMMUNICATION MODULE DL05/06 OPTION MODULE WITH MODBUS TCP $199.00
Anything else I'd need?
(footnote: 8 inputs will be more than enough. I selected the relay outputs thinking I could easily picture wanting to turn on a light or operate a solenoid valve. But that's not a requirement at the moment.)
Paul
On Sep 27, 2011, at 10:27 AM, Mark Rivers wrote:
The EPICS Modbus driver works fine with the Koyo PLCs, and I have tested reading ADCs with it.
Sent: Tue 9/27/2011 10:22 AM
To: [email protected]
Subject: Re: Simple ADC - Ethernet device?
Josh,
The price on the Koyo devices is appealing.
But the EPICS driver seems to be for serial communication, not ethernet.
Paul
On Sep 27, 2011, at 9:50 AM, Josh Stein wrote:
Although not purpose-built, we often use PLCs for simple analog acquisition. At APS the PLC-Direct brand (basically Koyo) is very ubiquitous.
On 9/27/11 9:38 AM, Paul Nord wrote:
I need to monitor the pressure in a gas supply bottle. We expect to need to change gas bottles every few days and we'd like to alert the detector operators in plenty of time.
Getting a transducer to produce a voltage is simple enough. I'm a little unclear about the next step: digitizing that voltage and getting that information to our EPICS softIOC. I'd like a simple box that connects to the voltage and also to an ethernet port.
There is an Epics driver for the environment monitor Websensor from Esensors Inc. It monitors temperature, humidity, and illumination. The device can also monitor a voltage reading. I presume it would be easy modify the driver to also get the voltage reading.
Is there another ethernet-based ADC that you would recommend?
There are some nice USB devices. But I don't really want to setup a computer just to monitor one voltage remotely.
I found some nice modular systems from Omega and NI. Alas, there are no Epics drivers.
Paul
Pete R. Jemian, Ph.D. <[email protected]>
Beam line Controls and Data Acquisition, Group Leader
Advanced Photon Source, Argonne National Laboratory
Argonne, IL 60439 630 - 252 - 3189
Education is the one thing for which people
are willing to pay yet not receive.
- Simple ADC - Ethernet device? Paul Nord
- Re: Simple ADC - Ethernet device? Josh Stein
- Re: Simple ADC - Ethernet device? Paul Nord
- RE: Simple ADC - Ethernet device? Mark Rivers
Re: Simple ADC - Ethernet device? David Dudley
<2011>
<2011>