1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  <20102011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  <20102011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Subject: Re: Timeout errors with ASYN Modbus Driver 2.0
To: EPICS tech-talk <[email protected]>
Date: Mon, 11 Oct 2010 17:10:22 -0400
Title: Re: Timeout errors with ASYN Modbus Driver 2.0
Have the packages that came with SynApps 5.5 installed.
Asyn is version 4.13
Modbus is 2.0
Yes, we’re reading several variables from the remotes.  I’m including one of the st.cmd files for the single modbus unit for reference.  I believe all the input devices are set for I/O Interrupt.
David
On 10/11/10 3:20 PM, "Mark Rivers" <[email protected]> wrote:
Hi David,
What version of asyn are you using?
Are these errors for input records?
How have you configured your asyn input drivers, i.e. how many polls per second?  Recall that input records do not actually cause any Modbus I/O to occur, they just get the values from the most recent poll.
What timeout are you specifying in your modbusInterportConfig command?  Have you tried increasing that?
From: [email protected] [mailto:[email protected]] On Behalf Of David Dudley
Sent: Monday, October 11, 2010 1:41 PM
To: EPICS tech-talk
Subject: Timeout errors with ASYN Modbus Driver 2.0
Mark,
We’re having problems with the Modbus 2 driver for ASYN
I have 2 sets of Modbus networks.  One network has a single device, connected from a MOXA 5130 RS-485 converter to a Siemens S7-200 PLC.   The other has the same Moxa 5130 MOXA converter with RS-485, connected to a Mirion Radiation monitor and a Apantec Radiation monitor.
Originally, I was using Modbus version 1.3 on the system with the S7-200 PLC.  It worked for almost a year before upgrading to Modbus 2.  After that system had been operating successfully, with no errors, for an extended period, I needed to upgrade the driver so that I could have 2 Modbus devices daisy-chained on a connection.  At the same time, in order to limit the number of software revisions in the field, the S7-200 PLC network was upgraded as well.
Occasionally, we get error messages similar to the following:
epics> 2010/10/11 14:30:05.262 drvModbusAsyn::doModbusIO port LPDU3 error calling writeRead, error=radmon5.nsls2.bnl.gov:4001 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2010/10/11 14:30:05.262 B-725:VUV<RadMon:2a>Dosage:2 devAsynInt32 process read error
2010/10/11 14:30:05.262 B-725:VUV<RadMon:2b>Dosage:2 devAsynInt32 process read error
2010/10/11 14:30:06.262 drvModbusAsyn::doModbusIO port LPDU3 has I/O error
2010/10/11 14:34:42.310 drvModbusAsyn::doModbusIO port RM1W error calling writeRead, error=radmon5.nsls2.bnl.gov:4001 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2010/10/11 14:34:42.310 B-725:VUV<RadMon:1>Dosage:2 devAsynInt32 process read error
2010/10/11 14:34:42.387 modbusInterpose::readIt, CRC error
2010/10/11 14:34:42.387 drvModbusAsyn::doModbusIO port LPDU3 error calling writeRead, error=radmon5.nsls2.bnl.gov:4001 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2010/10/11 14:34:42.387 B-725:VUV<RadMon:2a>Dosage:2 devAsynInt32 process read error
2010/10/11 14:34:42.387 B-725:VUV<RadMon:2b>Dosage:2 devAsynInt32 process read error
2010/10/11 14:34:43.310 drvModbusAsyn::doModbusIO port RM1W has I/O error
2010/10/11 14:34:43.387 drvModbusAsyn::doModbusIO port LPDU3 has I/O error
This only happens occasionally, and happens on both modbus networks, at asynchronous times.  All devices in the modbus chain are scanned once per second, and during the time that the errors are –not- occuring, the data stream retrieved is valid.  I’ve verified that data is being transmitted, but it looks like occasionally data is not being received and processed correctly.
Oh, and also, it only happens if the IOC is using Modbus 2.  Modbus 1.3 works without errors, but can only address a single device on each modbus network.
Any ideas of where to start looking?
David
David
"... The Crossbow Project. There's No Defense Like a Good Offense. " - Real Genius (1985)
Don't think it exists?  Google the Air Force X-37B project.
Attachment: st.cmd.zip
Description: video/flv
RE: Timeout errors with ASYN Modbus Driver 2.0 Mark Rivers
Prev: RE: Timeout errors with ASYN Modbus Driver 2.0 Mark Rivers
Next: Re: No HomeStatus and No Motion with OMS MAXv : Motor 6.5.1 / VxWorks 6.8 / base 3.14.11 Daron Chabot
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  <20102011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Next: RE: Timeout errors with ASYN Modbus Driver 2.0 Mark Rivers
ANJ, 12 Sep 2012 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·
