Ron,
In our case the problem is a little different. Back in 2006/7 after the
ID34 problem at APS we had all of our OMS58 cards modified by the vendor
including the card that failed this summer.
Elder
-----Original Message-----
Sent: Wednesday, October 21, 2009 9:06 AM
To: Elder Matias
Cc: [email protected]
Subject: Re: CLS OMS 58 Failure Report
Hello Elder,
This failure, and the vendor's fix, are documented in the following
tech-talk message;
http://www.aps.anl.gov/epics/tech-talk/2006/msg01261.php
From the above message;
> OMS VME58 user's should review what the consequences of
> having this failure occur at their facilities would be.
> The decision to have your boards retrofitted should strike
> a balance between the probability of board failure (higher
> if exposed to radiation) and the consequences of that
> failure.
Ron
Elder Matias wrote:
> I should have sent this failure report out some time ago in case it is
> helpful at one of the other labs.
> This summer we had an OMS58 board fail. The result of the failure was
a
> less than desirable outcome for one of our Kohzu monocromator.
> The nature of the failure is that on several channels this OMS58 board
> started sending pulses out to the motors, in complete disregard to any
> limit switches and without being commanded by the software. Without
any
> hard stops or secondary limit switches that interlock the drive power
> the motors continued moving beyond their normal range of travel and
did
> a bit of damage to the internals of the mono. In this application we
> were relying on the firmware (on the board) to stop the motion when
the
> limit switches were hit.
> We removed the board from the beamline, brought it back to our
controls
> test lab, were able to reproduce the failure in a different setup.
The
> board was shipped back to the supplier, they localized the failure to
a
> data buffer IC (74245) that is located in U82 on OMS58.
> Elder
- CLS OMS 58 Failure Report Elder Matias
- Re: CLS OMS 58 Failure Report Ron Sluiter
RE: CLS OMS 58 Failure Report Elder Matias
compiling streamDevice with CALC set fails Dr. Peter Zumbruch
<2009>
<2009>