Subject: RE: Waveform Records
To: "David Dudley" <[email protected]>, <[email protected]>
Date: Thu, 4 Sep 2008 14:14:45 -0400
Some issues ---
1) waveforms are just arrays. You're device support can fill it any way you like.
2) there is a circular buffer record that already does this either ring buffer - or successive averaging or keep high or low for each sample.
3) we do not queue the array - so if your client is not getting them fast enough in monitoring - then you will loose old arrays. You may even get half of one and half of another. This system needs to be set up carefully.
4) There is a subarray record for just reading an area of interest.
5) we did not do the meta data correctly - so no indication of the unit of time between samples within the array.
-----Original Message-----
Sent: Thu 9/4/2008 2:04 PM
To: [email protected]
Subject: Waveform Records
Need a little 'training' on waveform records....
1. With a waveform record, with each scan of the I/O device, does the
device read in a single sample, or a whole waveform?
2. Can waveforms be setup to operate in a continuous FIFO manner?  In
other words, a sliding window of data items collected over time?
3. Can 'edm' display a waveform record, and if so, how?  If 'edm' can't
display them, is there a program that can?