Subject: |
RE: Motion control failure at APS - Not a Problem for Hytec 8601 / 8909 |
"Darrell Nineham" <[email protected]> |
To: |
Date: |
Wed, 22 Nov 2006 14:45:34 -0000 |
Dear Tech-Talk Readers,
I have been asked to re-submit this tech-talk reply with the signature
removed, as it put restrictions on its publishing. Apologies to all.
Following Ron Sluiter's recent problems with motor limits, we would just
like to re-assure any users and potential users of Hytec Stepper Motor
drivers.
You might like to know that the motor drive system offered by Hytec and
in use at SLAC includes logic which prevents movement beyond a limit no
matter what the controller does, as a fail-safe measure. In fact if you
want to operate a system without limit switches you have to physically
wire them out (see page 8 of the 8909 document at the end of the link
below). They can not be disabled in software and electronically operate
in a fail safe (halt all movement) manner. Our controller, the SM8601
Industry Pack, also does not suffer from the defect found in the OMS
unit, in that it cannot produce step pulses except when the GO bit or
JOG bit is set; external resets just knock these bits down.
http://www.hytec-electronics.co.uk/8909_User_Manual_issue_1.pdf
http://www.hytec-electronics.co.uk/8601%20Product%20Specification_ISS%20
3.0.pdf
Darrell Nineham
Hytec Electronics Ltd.
Tel: +44 (0) 118 975 7770
Fax: +44 (0) 118 975 7566
Web: www.hytec-electronics.co.uk
-----Original Message-----
Sent: 13 November 2006 18:12
To: EPICS
Subject: Motion control failure at APS
On Tuesday, July 25, a serious motion control failure
occurred in the 34ID-A hutch here at the APS.
All eight stepper motors controlled by a single Oregon
Micro Systems (OMS) VME58 board ran past their limit
switches and into their mechanical stops.
The eight stepper motors involved in the accident are
used to position two white beam slits and a mirror.
Bellows up stream from the 1st white beam slit were
punctured by the x ray beam. Vacuum was lost.
Additional damage included two broken limit switches
and an ion pump.
Three days of beamtime were lost.
Like all APS beamlines using the OMS motor controllers,
this IOC relies on the OMS controller to stop motion
when a motor is moving in the direction of an activated
limit switch. In this case, not only did the OMS
controller fail to stop motion when the limit switches
were activated, the controller entered a strange failure
mode that drove the motors into their mechanical stops.
The VME crate in question is located inside the 34ID-A white-beam hutch.
It is possible that radiation damage contributed to the failure of the
OMS VME58 controller.
There are hundreds of OMS boards at APS that have been in operation for
many years, and no report of this type of failure has ever been made.
OMS has also never had a report of this type of failure.
Between Kurt Goetze, OMS and myself; we have determined
that the failure resulted from two characteristics of
the OMS VME58 board, that, together conspired to cause
this failure. First, we have known for some time that
the OMS VME58 boards output a step pulse on every axis
after a VMEbus reset. Second, (unknown to us) the
on-board VME58 watchdog can cause the board to go into
a continuous reset cycle if there is a board failure.
These two characteristics, together, caused the failed
VME58 board at 34ID-A to step all eight of its' motors at approximately
4 steps per second until power was shut off.
Since this accident OMS has resolved the "step pulse on
reset" problem. By fixing the "step pulse on reset" problem, OMS
prevents the VME58 from accidentally driving its' motors if a board
fails and exhibits the "continuous reset" behavior.
The "fix" requires the replacement of nine socketed
components on the VME58 controller board.
OMS is providing two ways to retrofit VME58 boards with
this fix.
Option #1 - Send your VME58 boards back to OMS. They will replace the
nine components and retest the board. To do this, first contact OMS for
a Return Materials Authorization
(RMA) number and refer to Engineering Waver #112 (EW112)
as the reason for the RMA. Cost is $357.00 per board.
Option #2 - OMS is providing a retrofit kit that includes
the nine parts (5 of which are pre-programmed), labeling, instructions
and shipment for $107 per kit.
I don't have the specifics on how to order the kit. I will post that
info. in a follow-up message.
If you are ordering new OMS VME58 boards, be aware that OMS will not be
incorporating the upgrade chip set unless you specify Engineering Waiver
no. 112 (EW112) in your order. In addition, we recommend the MAXv rather
than the VME58 for new orders.
For those who choose to upgrade existing VME58 boards,
I strongly advise option #1. Option #2 opens you to the
risk of taking a perfectly functioning VME58 board and
making it less reliable; e.g., bending a pin while inserting
a part in a socket or damage from static discharge. Option
#1 provides full testing and quality assurance from OMS.
Closing thoughts;
- Thanks to OMS for addressing and fixing this problem.
The VME58 product family is approaching it's end of life.
The only incentive for OMS to devote resources to resolving this problem
is their commitment to quality.
- The "step on reset" problem does not occur in OMS's
latest controller; the MAXv and MAXp controllers.
- OMS VME58 user's should review what the consequences of having this
failure occur at their facilities would be. The decision to have your
boards retrofitted should strike a balance between the probability of
board failure (higher if exposed to radiation) and the consequences of
that failure.
Sorry for the length; hope I didn't bore you,
Ron
RE: Motion control failure at APS - Not a Problem for Hytec 8601 / 8909 Darrell Nineham
Naming conventions for devices and Epics records (more ...) Lecorche Eric
<2006>
Re: Building and testing Libera EPICS Andrew Johnson
<2006>
