1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  <20042005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  <20042005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Subject: RE: Bidirectional device support
To: <[email protected]>, <[email protected]>, <[email protected]>, <[email protected]>
Date: Mon, 12 Apr 2004 10:02:28 -0600
It may very well be an issue of personnel preference and design
philosophy.  On our machine it comes up on a lot of equipment.
The key issue is that you can walk up to a power supply or another
intelligent device switch the device to local mode change the set point
(on its local panel) and then put the device back into remote (EPICS)
control mode.  At this point there is an inconsistency because EPICS is
running with a different set point than the device in the field.  This
is independent of how you handle the readback.
As an example:
	In the control room I set a power supply to 20 Amps.
		EPICS SP= 20 Amp, PS SP = 20 Amp, feedback = 20 Amp.
	Go to the local PS panel place the device in local and change to
30 Amps
		EPICS SP = 20 Amp, PS SP = 30 Amp, feedback = 30 Amp.
	Place the device into remote
The end result is the poor operator in the control room is left
scratching his head because he is looking at a screen that says the
device is being commanded to be at 20 Amps, the feedback says it is at
30 Amps.
As for the concern about someone changing the setpoint in the field and
at an OPI at the same time, this is the nature of a distributed control
system.  This problem is no different than two people changing a value
on two different OPIs at the same moment in time.
Elder
To: "Thompson, David H." <[email protected]>, Andrew Johnson
<[email protected]>, tech-talk <[email protected]>
Date: Mon, 12 Apr 2004 10:56:43 -0400
I think the desire for bidirectional records reflects some personal
preference; some people think there is some kind of elegance about it.
I
agree with Andrew that it is not realistic.  I think it can be easily
avoided
in all cases, as I outline below.
>===== Original Message From "Thompson, David H." <[email protected]>
>If you are trying to do I/O on the same point you are right.  You can't
>really turn most hardware around like that anyway.  There are two or
>three cases that I think we (at SNS) need to be able to do
>bi-directional I/O; when talking to a smart device and you want to do
>bumpless transfer of control between local and remote,
This sounds equivalent to having a remote/local switch on the device;
the
switch is implemented in labview.  I thought it was SNS policy to not
have
EPICS control remote/local switches.  These should be controlled at the
device
(locally).  EPICS reads them.  Some poor guy locally testing the
hardware
should not have control taken away from the control room.  Its not safe.
[>]when you have a
>device that can set one state and depends on Epics to set the other
>state,
For this you have an output record that sets it and a readback record
that
reads it.  I find the least confusing way to do this is to have the
output
record be momentary, ie, a bo with a HIGH of about 1 so that when you
push the
button it sets the state (which is read out) and returns to standby.
[>]and when you have more than one PV pointing at the same hardware
>address in the OUT field.
In this case, last gets it. This just says you monitor the val field.
The
difference from the normal case is that all device supports which write
to the
same hardware must post monitors when any of them controls it.  Its not
really
bidirectional control.
Carl
Carl Lionberger
SNS Controls Group
(865) 574-7636
Prev: RE: Bidirectional device support Carl Lionberger
Next: RE: Bidirectional device support Purcell, J. David
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  <20042005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024