1994  1995  1996  1997  1998  1999  2000  <20012002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  Index 1994  1995  1996  1997  1998  1999  2000  <20012002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024
Subject: Re: CA connect delays under Windows
To: [email protected]
Cc: [email protected]
Date: Mon, 23 Jul 2001 17:00:33 -0600
Hello:
Mark Rivers found an interesting delay in CA on Win32.
The crux is that CA does not really need DNS. As I understand,
it only uses it so that it can produce pretty error messages.
Instead of "trouble with 123.45.67.98" you see "trouble with some.ioc.at.your.site.org"
because at connection time CA tries to get a name for each peer.
The necessary gethostbyaddr (or whatever) is what caused Mark's delay, it might cause a total
hangup when starting e.g. medm while the DNS server is down.
I understand this has been changed for CA in R3.14:
CA will no longer try to show the DNS name but only the IP address.
-Kay
At 04:02 PM 7/23/2001, Mark Rivers wrote:
>Folks,
>We have discovered an interesting problem which may save others some grief
>to know about.
>On the BioCAT sector at the APS they found that they could connect from Unix
>machines to their IOCs with no problems, there is no noticeable delay on a
>"caget" for example. However, Windows clients all had a 6 second delay in
>each clent application whenever a connection was made to the first PV in a
>given IOC.  Subsequent PVs in the same IOC connected "instantly" in the same
>invocation of the same client application (e.g. "probe").  This delay was
>seen on all clients on Windows 98, Windows NT and Windows 2000.  The delay
>was NOT seen when connecting from these same Windows machines to IOCs on
>other subnets.
>We put a sniffer on the subnet and found the following:
>- Windows client broadcast a CA UDP request
>- IOC answered with a UDP response within 2 msec.
>- However, the Windows machine then sent a series of 3 requests to port 137,
>followed by a "Bad port" reply from the IOC.  Port 137 is a netBios port.
>These requests were exactly 1.50 seconds apart.  After a final 1.50 second
>delay the TCP conversation took place and the CA connection completed.  This
>explains the 6 second delay seen on each invocation of any CA client.
>The problem turned out to be that the IOCs did not have DNS entries.  This
>did not matter to the Unix clients, but it appears that if there is not a
>DNS entry for an IOC then Windows attempts to communicate on port 137 (to
>determine machine's identity?), and this results in 6 second delays in CA
>connections.
>As soon as the DNS server was updated to include entries for the IOCs the
>delays disappeared and everything worked fine.
>Bottom line: make sure your IOCs have DNS entries if you are going to use
>Windows!
>Cheers,
>Mark Rivers