1. License
This document is distributed under the terms of the GNU Free Documentation License, version 1.2.
2. Document History
Revision Date Author Section Modification
1.0
2003-12-12
Klemen Žagar
all
Created.
1.1
2004-01-08
Aleš Pucelj
all
Finalized structure.
2004-01-10
Matej Šekoranja
all
Review.
1.2
2004-04-19
Aleš Pucelj
all
Draft completed.
1.3
2004-05-31
Aleš Pucelj
all
Matej’s comments considered (after Channel Access for Java implementation).
2004-06-01
Matej Šekoranja
all
Review.
2004-08-12
Klemen Žagar
all
Released
1.4
2008-02-07
Matej Šekoranja
all
Description of CA_PROTO_READ and CA_PROTO_READ_SYNC added.
2008-02-07
Klemen Žagar
all
Released
1.4.1
2014-08-27
Daniel J. Lauk
all
Transformed to AsciiDoc format. Recreated graphics.
1.5
2014-09
Michael Davidsaver
all
Major revision to describe operation semantics
3. Introduction
This document describes the EPICS Channel Access (CA) protocol as it is, and has been, implemented. It is also intended to act as a specification to allow the creation of new client and server implements. The focus is on versions >= 4.11 of the CA protocol, which used by EPICS Base 3.14.0 and later. No changes from protocol versions before 4.8 (EPICS Base 3.13.0) will be included in this document.
For the benefit of those writing new clients and servers RFC 2119:Key words for use in RFCs to Indicate Requirement Levels are used.
4. Concepts
4.1. Process Variables
A Process Variable (PV) is the addressable unit of data accessible through the Channel Access protocol. Each PV has a unique name string and SHOULD be served by a single Channel Access server. Specifically, when searching for a PV, each client MUST NOT receive replies identifying more than one server.
4.2. Virtual Circuit
A TCP connection between a CA client and server is referred to as a Virtual Circuit.
Typically only one Circuit is opened between each client and server. However, a client MAY open more than one Circuit to the same server.
4.2.1. TCP Message Flow
The following tree diagram illustrates the order in which normal (not error) CA messages can be sent on a TCP connection. Nodes with box borders are messages sent be the server, and oval borders are messages sent be the client. Nodes with a double border (eg. "Open Socket") are not themselves messages. Instead they indicate pre-conditions which must be meet before certain messages can be sent.
The message CA_ERROR may be sent by a server in response to any client message.
Virtual Circuit message flow
4.3. Channels
A Channel is the association between a particular Circuit and PV name.
At core, a Channel is a runtime allocated pair of integer identifiers (CID and SID) used in place of the PV name to avoid the overhead of string operations. Both client and server MUST maintain a list of the identifiers of all open Channels associated with a Circuit.
The scope of these identifiers is a single Circuit. Identifiers from one Circuit MUST NOT be used on any other. Further more, the same identifier number may be used one two different Circuit in connection with two different PV names.
A Channel’s identifiers are explained in section Message Identifiers.
4.4. Monitors
A monitor is created on a channel as a means of registering/subscribing for asynchronous change notifications (publications). Monitors may be filtered to receive only a subset of events (Event Mask), such as value or alarm changes. Several different monitors may be created for each channel.
Clients SHOULD NOT create two monitors on the same channel with the same Event Mask.
4.5. Server Beacons
Server beacons messages (CA_PROTO_RSRV_IS_UP) MUST be periodically broadcast. Beacon messages contain the IP address and TCP port on which the server listens A sequential beacon ID is also included.
When a server becomes active, it MUST immediately begin sending beacons with an increasing delay. An initial beacon interval of 0.02 seconds is RECOMMENDED. After each beacon is sent the interval SHOULD be increased up to a maximum interval. Doubling the interval is RECOMMENDED. The RECOMMENDED maximum interval is 15 seconds.
As a server sends beacons it MUST increment the BeaconID field for each message sent.
CA clients MAY use a server’s first beacon as a trigger to re-send previously unanswered CA_PROTO_SEARCH messages.
While it was done historically, clients SHOULD NOT use Beacons to make timeout decisions for TCP Circuits. The CA_PROTO_ECHO message should be used instead.
Clients wishing to detect new servers should maintain a list of all servers along with the last BeaconID received, and the reception time. Servers SHOULD be removed from this list when no Beacon is received for some time (two beacon periods is RECOMMENDED).
4.6. Repeater
4.7. Timeout Behavior
CA clients typically SHOULD NOT automatically reconnect Circuits which have become unresponsive, instead CA clients SHOULD send a new CA_PROTO_SEARCH request.
CA clients SHOULD on occasion re-send PV name searches which are not answered.
Care must be taken to avoid excessive network load due to repeated lookups and connections. Clients are RECOMMENDED to implement an exponentially increasing (up to a maximum) interval when re-sending CA_PROTO_SEARCH messages for each PV.
Clients are RECOMMENDED to implement a timeout before re-starting a search when a Channel is closed due to an Exception, or Channel creation fails with CA_PROTO_CREATE_CH_FAIL reply.
4.8. Version compatibility
Certain aspects of Channel Access protocol have changed between releases. In this document, Channel Access versions are identified using CA_VXYY, where X represents single-digit major version number and YY represents a single- or double-digit minor version number. Stating that a feature is available in CA_VXYY implies that any client supporting version XYY must support the feature. Implementation must be backward compatible with all versions up to and including its declared supported minor version number.
Example 1. Channel Access version number
CA_V43, denotes version 4.3 (major version 4, minor version 3).
Channel Access protocol carries an implicit major version of 4. Minor version begin with 1. Minor version 0 is not a valid version.
When a Virtual Circuit is created both client and server send their minor version numbers. The valid messages and semantics of the Circuit are determined by the lower of the two minor versions.
A partial history of CA minor version changes:
EPICS Base CA Minor Year Reason
3.14.12
13
Dynamic array size in monitors
3.14.12
12
PV search over tcp
3.14.0-b2
11
large array?, circuit priority?
3.14.0-b2
10
Beacon counter???
3.14.0-b1
9
Large packet header
3.13.0-b10
8
3.13.0-a5
7
Start of CVS history
4.9. Exceptions
Channel Access protocol error messages (CA_PROTO_ERROR) are referred to as Exceptions. Exceptions are sent by a CA server to indicate its failure to process a client message.
An Exception MAY be sent in response to any client message, including those which normally would not result in a reply.
Exception messages carry the header of the client message which triggered the error. It is therefore always possible to associate an Exception with the request which triggered it.
5. Operation
5.1. Overall Server Operation
A CA server will maintain at least two sockets.
A UDP socket bound to the CA port (def. 5064) MUST listen for PV name search request broadcasts. PV name search replies are sent as unicast messages to the source of the broadcast. This socket, or another UDP socket, SHOULD periodically send Beacons to the CA Beacon port (def. 5065).
A TCP socket listening on an arbitrary port. The exact port number is included in PV name search replies. This socket will be used to build Virtual Circuits.
A CA server SHOULD NOT answer PV name search requests for itself unless a CA_PROTO_CREATE_CHAN for that PV from the same client can be expected to succeed. To do otherwise risks excessive load in a tight retry loop.
5.2. Overall Client Operation
A CA client SHOULD maintain a registration with a Repeater on the local system, (re)starting it as necessary.
Clients will send PV name search messages and listen for replies. Typically a client will maintain a table of unanswered name searches and a cache of recent results in order avoid duplicate searches, and to process any replies.
Once an affirmative search reply is received, a Virtual Circuit to the responder is opened if needed. If the client already has a circuit open to this server, it SHOULD be reused. When a Circuit is available, a Channel is created on it, then various get/put/monitor operations are performed on this Channel.
5.3. Name Searching
The process of finding the server which advertises a PV to a particular client can be carried out over UDP, or with >= CA_V412 over a TCP connection.
In either case each client SHOULD be pre-configured with a set of destinations to send queries. For UDP searching, this is a list of unicast or broadcast endpoints (IP and port). For TCP searching, this is a list of endpoints.
It is RECOMMENDED that a default set of UDP endpoints be populated with the broadcast addresses of all network interfaces except the loopback.
It is RECOMMENDED that, on client startup, Circuits be established to all endpoints in the TCP search list.
Search results are transitory. Subsequent searches MAY yield different results. Therefore queries SHOULD be re-tried unless an active Channel is already open.
5.3.1. UDP search datagrams
Several CA messages MAY be included in one UDP datagram.
A datagram which includes CA_PROTO_SEARCH messages MUST begin with a CA_PROTO_VERSION message.
For efficiency it is RECOMMENDED to include as many search requests as possible in each datagram, subject to datagram size limits.
A CA server MUST NOT send a CA_PROTO_NOT_FOUND in response to a UDP search request.
CA_PROTO_SEARCH messages MUST NOT be sent on a Circuit unless a CA_PROTO_VERSION message has been received indicating >= CA_V412.
When supported, CA_PROTO_SEARCH messages may be sent at any time the circuit is open.
A CA server MAY send a CA_PROTO_NOT_FOUND in response to a UDP search request if the DO_REPLY bit is set.
Clients MAY ignore CA_PROTO_NOT_FOUND messages.
A CA_PROTO_NOT_FOUND message is not final. A subsequent search might yield a different result.
5.4. Virtual Circuits
5.4.1. Inactivity timeout
When a Circuit is created, both client and server MUST begin a countdown timer. When any traffic (including a CA_PROTO_ECHO message) is received on the Circuit, this counter is reset to its initial value. If the timer reaches zero, the Circuit is closed.
Clients MUST send a CA_PROTO_ECHO message before the countdown reaches zero. It is RECOMMENDED to send an echo message when the countdown reaches half its initial value.
When a CA_PROTO_ECHO message is received by the server, it MUST be immediately copied back to the client.
The RECOMMENDED value for the countdown timer is 30 seconds.
5.4.2. Circuit Setup
When a Circuit is created, both client and server MUST send CA_PROTO_VERSION as their first message. This message SHOULD be sent immediately.
Note for implementers. For EPICS Base before 3.14.12, RSRV did not immediately send a version message due to a buffering problem. Instead the version message was not sent until some other reply forced a flush of the send queue.
In addition the client SHOULD send CA_PROTO_HOST_NAME and CA_PROTO_CLIENT_NAME messages. Once this is done, the Circuit is ready to create channels.
Note that the host and client name messages SHOULD NOT be (re)sent after the first channel is created. If the client or host name strings change, the circuit SHOULD be closed.
If no host or client name messages are received a server MUST consider the client to be anonymous. It is RECOMMENDED that anonymous users not be granted rights for the Put operation.
5.4.3. Channel Creation
Channel creation starts with a CA_PROTO_CREATE_CHAN request from the client. This message includes the PV name string, and a client selected CID.
If the server can not provide the named PV it replies with CA_PROTO_CREATE_CH_FAIL using the same CID. The server MUST NOT remember the CID of failed creation requests as clients MAY re-used them immediately.
If the server can provide the named PV, it replies with CA_PROTO_ACCESS_RIGHTS followed by a CA_PROTO_CREATE_CHAN reply. Further CA_PROTO_ACCESS_RIGHTS messages MAY follow to reflect changes to access permissions.
Note that the CA_PROTO_CREATE_CHAN reply includes the Channel’s native DBR datatype and the maximum number of elements which can be retrieved/set by a get, put, or monitor operation. These attributes are fixed for the lifetime of the channel.
The reply also contains the server selected SID identifier. Together with the CID, these two identifier will be used to refer to the Channel in subsequent operations.
The Channel remains active, and the identifiers valid, until a CA_PROTO_CLEAR_CHANNEL request is sent by a client and its reply received, until a CA_PROTO_SERVER_DISCONN message is received by a client, or if the circuit (TCP connection) is closed.
After a server sends a CA_PROTO_CLEAR_CHANNEL reply or a CA_PROTO_SERVER_DISCONN message it MAY reuse the SID immediately.
After a client receives a CA_PROTO_CLEAR_CHANNEL reply or a CA_PROTO_SERVER_DISCONN message it MAY reuse the CID immediately.
Therefore after a client sends a CA_PROTO_CLEAR_CHANNEL request, or a sever sends a CA_PROTO_SERVER_DISCONN request, no further messages (including CA_PROTO_ERROR) should be sent for the closed channel.
5.4.4. Put Operations
A Operation to write data to a Channel begins with a CA_PROTO_WRITE or CA_PROTO_WRITE_NOTIFY request. The difference between the two is that CA_PROTO_WRITE_NOTIFY gives a reply on success, while CA_PROTO_WRITE does not.
The CA_PROTO_WRITE SHOULD be used when it is not important that all Put operations are executed. A server SHOULD make best effort to ensure that, when a burst of CA_PROTO_WRITE requests is received, that the last request is processed (others could be dropped).
A CA_PROTO_WRITE_NOTIFY request indicates that the client intends to wait until the request is fulfilled before continuing. A server MUST reply to all CA_PROTO_WRITE_NOTIFY requests. A server SHOULD make best effort to fully process all CA_PROTO_WRITE_NOTIFY requests.
Both request messages include a SID to determine which Channel is being operated on.
In addition, a client selected IOID is included. This identifier will be included in a CA_PROTO_WRITE_NOTIFY reply, as well as any CA_PROTO_ERROR exception message resulting from a Put request.
5.4.5. Get Operation
The present value of a Channel is queried with a CA_PROTO_READ_NOTIFY request.
A server MUST reply to all CA_PROTO_READ_NOTIFY requests. A server SHOULD make best effort to fully process all CA_PROTO_READ_NOTIFY requests.
CA_PROTO_READ_NOTIFY messages include a SID to determine which Channel is being operated on, as well as a client selected IOID which will be included in the reply.
The IOID MUST be unique on the channel.
5.4.6. Monitor Operation
A Monitor operation is a persistent subscription which is initiated by a CA_PROTO_EVENT_ADD request and terminated with a CA_PROTO_EVENT_CANCEL request.
Both CA_PROTO_EVENT_ADD and CA_PROTO_EVENT_CANCEL messages include a channel SID as well as a client selected SubscriptionID.
The SubscriptionID MUST be unique on the channel.
When a subscription is created a server SHOULD immediately send a CA_PROTO_EVENT_ADD reply with the present value of the Channel if such a value is available.
After a CA_PROTO_EVENT_CANCEL request is received, a server MUST send one final CA_PROTO_EVENT_ADD reply with a zero payload size. Before a CA_PROTO_EVENT_CANCEL request is received, a server MUST NOT send a CA_PROTO_EVENT_ADD reply with a zero payload size.
5.4.7. Errors
Any client message MAY result in an CA_PROTO_ERROR reply from a server.
5.5. Data Count in Gets and Monitors
Prior to CA_V413, the element count in a CA_PROTO_EVENT_ADD or CA_PROTO_READ_NOTIFY reply MUST be the same as given in the corresponding CA_PROTO_EVENT_ADD or CA_PROTO_READ_NOTIFY request. A request for zero elements MUST result in an ECA_BADCOUNT exception. If a server can not provide all of the elements requested, then it fills out the message body with null bytes.
Beginning in CA_V413, a request for zero elements is valid. The element count in a reply is then the number of elements the server could provide (perhaps zero).
The element count in a reply MUST NOT exceed the maximum element count on the channel.
This dynamic array size feature creates a potential ambiguity in the protocol if the number of bytes in a CA_PROTO_EVENT_ADD reply is zero.
Therefore it is RECOMMENDED that clients not create dynamic monitors for the plain DBR_* types. Clients needing to create such monitors are RECOMMENDED to promote the type to the corresponding DBR_STS_* (the extra meta-data can be ignored for internal processing). Then a zero element count has a non-zero body size.
Note to implementers. RSRV will always give at least one element in CA_PROTO_EVENT_ADD replies. libca will silently ignore CA_PROTO_EVENT_ADD replies with zero size before a CA_PROTO_EVENT_CANCEL request is received.
6. Data Types
This section defines all primitive data types employed by CA, as well as their C/C++ equivalents. These data types are referred to in the subsequent sections.
Type Name C/C++ Description
BYTE
char
Signed 8-bit integer.
UBYTE
unsigned char
Unsigned 8-bit integer.
INT16
short
Signed 16-bit integer.
UINT16
unsigned short
Unsigned 16-bit integer.
INT32
int
Signed 32-bit integer.
UINT32
unsigned int
Unsigned 32-bit integer.
FLOAT
float
IEEE 32-bit float.
DOUBLE
double
IEEE 64-bit float.
STRING[n]
char[]
Array of UBYTE`s. If `[n] is specified, it indicates maximum allowed number of characters in this string including (if neccessary) termination character.
TIMESTAMP
None
Timestamp represented with two UINT32 values. First is number of seconds since 0000 Jan 1, 1990. Second is number of nanoseconds within second
All values are transmitted over the network in big-endian (network) order. For example: UINT32 3145 (0x00000C49) would be sent over the network represented as 00 00 0C 49.
7. Messages
7.1. Message Structure
All Channel Access messages are composed of a header, followed by the payload.
Header is always present. The command ID and payload size fields have a fixed meaning. Other header fields carry command-specific meaning. If a field is not used within a certain message, its value MUST be zeroed.
Total size of an individual message is limited. With CA versions older than CA_V49, the maximum message size is limited to 16384 (0x4000) bytes. Out of these, header has a fixed size of 16 (0x10) bytes, with the payload having a maximum size of 16368 (0x3ff0) bytes.
Versions CA_V49 and higher may use the extended message form, which allows for larger payloads. The extended message form is indicated by the header fields Payload Size and Data Count being set to 0xffff and 0, respectively. Real payload size and data count are then given as UINT32 type values immediately following the header. Maximum message size is limited by 32-bit unsigned integer representation, 4294967295 (0xffffffff). Maximum payload size is limited to 4294967255 (0xffffffe7).
For compatibility, extended message form should only be used if payload size exceeds the pre-CA_V49 message size limit of 16368 bytes.
7.1.1. Header
Table 1. Standard Message Header
0 1 2 3 4 5 6 7
Command
Payload size
Data type
Data count
Parameter 1
Parameter 2
Table 2. Extended Message Header
0 1 2 3 4 5 6 7
Command
0xFFFF
Data type
0x0000
Parameter 1
Parameter 2
Payload size
Data count
Names of header fields are based on their most common use. Certain messages will use individual fields for purposes other than those described here. These variations are documented for each message individually. All of values in header are unsigned integers.
Generic header fields:
Parameter Type Description
Command
UINT16
Identifier of the command this message requests. The meaning of other header fields and the payload depends on the command.
Payload Size
UINT16 or UINT32
Size of the payload (in bytes). MUST not exceed 0x4000 for UDP.
Data Type
UINT16
Identifier of the data type carried in the payload. Data types are defined in section Payload Data Types.
Data Count
UINT16 or UINT32
Number of elements in the payload.
Parameter 1
UINT32
Command dependent parameter.
Parameter 2
UINT32
7.1.2. Payload
The structure of the payload depends on the type of the message. The size of the payload matches the Payload Size header field.
Message payloads MUST be padded to a length which is a multiple of 8 bytes. Zero padding is RECOMMENDED.
7.2. Message Identifiers
Some fields in messages serve as identifiers. These fields serve as identification tokens in within the context of the a circuit (TCP connection). The RECOMMENDED scheme for allocating these values is to create them sequentially starting at 0. All IDs are represented with UINT32.
Overflow of all identifiers MUST be handled! A long running applications might use more than 2**32 of some identifier type type (typically IOID).
7.2.1. CID - Client ID
A CID is the client selected identifier for a channel. A CID MUST be unique for a single Circuit.
Clients MUST not send a request with a CID which is not associated with an active Channel.
Servers MUST ignore any request which does not include the CID of an active channel without closing the Circuit.
A CID is found in the Parameter 1 field of CA_PROTO_ERROR, CA_PROTO_CREATE_CHAN, CA_PROTO_ACCESS_RIGHTS, CA_PROTO_CREATE_CH_FAIL, and CA_PROTO_SERVER_DISCONN messages. And in the Parameter 2 field of CA_PROTO_CLEAR_CHANNEL message.
7.2.2. SID - Server ID
A SID is the server selected identifier for a channel. A SID MUST be unique for a single Circuit.
Servers MUST not send a request with a SID which is not associated with an active Channel.
Clients MUST ignore any request which does not include the SID of an active channel without closing the Circuit.
7.2.3. Subscription ID
A SubscriptionID is the client selected identifier for a subscription. A CID MUST be unique for a single Circuit.
A SubscriptionID is found in the Parameter 2 field of CA_PROTO_EVENT_ADD and CA_PROTO_EVENT_CANCEL messages.
7.2.4. IOID
An IOID is the client selected identifier for a Get or Put operation. An IOID MUST be unique for a single message type on a single Circuit.
It is possible though NOT RECOMMENDED to use the same IOID concurrently in a CA_PROTO_WRITE, a CA_PROTO_READ_NOTIFY, and a CA_PROTO_WRITE_NOTIFY request.
An IOID is found in the Parameter 2 field of CA_PROTO_READ_NOTIFY, CA_PROTO_WRITE_NOTIFY, and CA_PROTO_WRITE messages.
7.2.5. Search ID
A SearchID is a client selected identifier for a PV name search. A SearchID must be unique for each client endpoint sending requests.
Due to the nature of UDP it is possible for datagrams to be duplicated. Several CA_PROTO_SEARCH messages with the same SearchID MAY be considered to be duplicates, and only one used.
8. Commands (TCP and UDP)
The following commands are sent as either UDP datagrams or TCP messages. Some of the messages are also used within the context of a Virtual Circuit (TCP connection).
8.1. CA_PROTO_VERSION
Command
CA_PROTO_VERSION
ID
0 (0x00)
Description
Exchanges client and server protocol versions and desired circuit priority. MUST be the first message sent, by both client and server, when a new TCP (Virtual Circuit) connection is established. It is also sent as the first message in UDP search messages.
8.1.1. Request
Table 3. Header
Field Value Description
Command
0
Command identifier for CA_PROTO_VERSION.
Payload size
0
Must be 0.
Priority
Desired priority
Virtual circuit priority.
Version
Version number
Minor protocol version number. Only used when sent over TCP.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Table 4. Compatibility
Version Comment
>= CA_V411
Server will send response immediately after establishing a virtual circuit.
< CA_V411
Message does not include minor version number (it is always 0) and is interpreted as an echo command that carries no data. Version exchange is performed immediately after CA_PROTO_CREATE_CHAN.
Comments
  • Priority indicates the server’s dispatch scheduling priority which might be implemented by a circuit dedicated thread’s scheduling priority in a preemptive scheduled OS.
  • Due to a buffering bug, RSRV implementing < CA_V411 did not send CA_PROTO_VERSION immediately on connection, but rather when some other other response triggers a buffer flush.
8.1.2. Response
Table 5. Header
Command
0
Reserved
0
Must be 0.
Priority
0
Must be 0.
Version
Version number
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Table 6. Compatibility
Version Comment
>= CA_V411
Server will not respond to request, but send response immediately after establishing a virtual circuit.
< CA_V411
Message does not include minor version number (it is always 0).
Command
CA_PROTO_SEARCH
ID
6 (0x06)
Description
Searches for a given channel name. Sent over UDP or TCP.
8.2.1. Request
Table 7. Header
Command
6
Command identifier for CA_PROTO_SEARCH.
Payload Size
>= 0
Padded size of channel name.
Reply
Reply Flag
Search Reply Flag, indicating whether failed search response should be returned.
Version
Version Number
Client minor protocol version number.
SearchID
Client allocated Search identifer.
SearchID
Table 8. Payload
Name Type Value Description
Channel name
STRING
Name of channel to search for.
Comments
  • Sent as a UDP datagram.
  • It is illegal to specify DO_REPLY flag whenever the message is sending as UDP datagram, regardless of whether broadcast or multicast is used.
  • SearchID will be allocated by the client before this message is sent.
  • SearchID field value is duplicated.
  • Reply flag will be generally DONT_REPLY when searching using broadcast and DO_REPLY when searching using unicast. When DO_REPLY is set, server will send a CA_PROTO_NOT_FOUND message indicating it does not have the requested channel.
8.2.2. Response
Table 9. Header
Command
6
Payload Size
8
Payload size is constant.
Data Type
Port number
TCP Port number of server that responded.
Data Count
0
Must be 0.
SID or IP
0xffffffff
Temporary SID (deprecated) or server IP address.
SearchID
Table 10. Payload
Server protocol version
UINT16
Server protocol version.
Comments
  • Received as UDP datagram.
  • Search ID field value (CID) is copied from the request.
  • Before CA_V411 the SID/IP field will always have the value of 0xffffffff and the server IP address is assumed to be the senders IP.
  • Starting with CA_V411 the server’s IP address is encoded in the SID/IP field if it differs from the sender’s IP, or 0xffffffff if it is the same.
  • The port number included in the header is the TCP port of the server. Two servers on the same host can share a UDP port number, but not a TCP port number. Therefore, the port the client needs to connect to in that situation may not be the same as expected if this field in the response is not used.
8.3. CA_PROTO_NOT_FOUND
Command
CA_PROTO_NOT_FOUND
ID
14 (0x0E)
Description
Indicates that a channel with requested name does not exist. Sent in response to CA_PROTO_SEARCH, but only when its DO_REPLY flag was set. Sent over UDP.
8.3.1. Response
Table 11. Header
Command
14
Command identifier for CA_PROTO_NOT_FOUND.
Reserved
0
Must be 0.
Reply Flag
DO_REPLY
Same reply flag as in request: always DO_REPLY.
Version
Same as request
SearchID
SearchID
Comments
  • Contents of the header are identical to the request.
  • SearchID fields are diplicated.
  • Original request payload is not returned with the response.
8.4. CA_PROTO_ECHO
Command
CA_PROTO_ECHO
ID
23 (0x17)
Description
Connection verify used by CA_V43. Sent over TCP.
8.4.1. Request
Table 12. Header
Command
23
Command identifier for CA_PROTO_ECHO.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
8.4.2. Response
Table 13. Header
Command
23
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
9. Commands (UDP)
The following commands are sent as UDP datagrams.
9.1. CA_PROTO_RSRV_IS_UP
Command
CA_PROTO_RSRV_IS_UP
ID
13 (0x0D)
Description
Beacon sent by a server when it becomes available. Beacons are also sent out periodically to announce the server is still alive. Another function of beacons is to allow detection of changes in network topology. Sent over UDP.
9.1.1. Response
Table 14. Header
Command
13
Command identifier for CA_PROTO_RSRV_IS_UP.
Reserved
0
Must be 0.
Version
Version number
CA protocol version
Server port
>= 0
TCP Port the server is listening on.
BeaconID
Sequential integers
Sequential Beacon ID.
Address
0 or IP
May contain IP address of the server.
Comments
  • IP field may contain IP of the server. If IP is not present (field Address value is 0), then IP may be substituted by the receiver of the packet (usually repeater) if it is capable of identifying where this packet came from. Any non-zero address must be interpreted as server’s IP address.
  • BeaconIDs are useful in detecting network topology changes. In certain cases, same packet may be routed using two different routes, causing problems with datagrams. If multiple beacons are received from the same server with same BeaconID, multiple routes are the cause.
  • If a server is restarted, it will most likely start sending BeaconID values from beggining (0). Such situation must be anticipated.
9.2. CA_REPEATER_CONFIRM
Command
CA_REPEATER_CONFIRM
ID
17 (0x11)
Description
Confirms successful client registration with repeater. Sent over UDP.
9.2.1. Response
Table 15. Header
Command
17
Command identifier for CA_REPEATER_CONFIRM.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Repeater address
IP address
Address with which the registration succeeded.
Comments
  • Since repeater can bind to different local address, its IP is reported in Repeater address. This address will be either 0.0.0.0 or 127.0.0.1.
9.3. CA_REPEATER_REGISTER
Command
ID
24 (0x18)
Description
Requests registration with the repeater. Repeater will confirm successful registration using CA_REPEATER_CONFIRM. Sent over TCP.
9.3.1. Request
Table 16. Header
Command
Command identifier
Reserved
0
Must be 0
Reserved
0
Must be 0
Reserved
0
Must be 0
Reserved
0
Must be 0
Client IP address
IP address
IP address on which the client is listening
10. Commands (TCP)
The following commands are used within the context of Virtual Circuit and are sent using TCP.
10.1. CA_PROTO_EVENT_ADD
Command
CA_PROTO_EVENT_ADD
ID
1 (0x01)
Description
Creates a subscription on a channel, allowing the client to be notified of changes in value. A request will produce at least one response. Sent over TCP.
10.1.1. Request
Table 17. Header
Command
1
Command identifier for CA_PROTO_EVENT_ADD
Payload Size
16
Data Type
Desired DBR type of the return value.
Data Count
>= 0
Desired number of elements
SID
SID of the channel.
SID of the channel on which to register this subscription. See SID - Server ID.
SubscriptionID
Client provided Subscription ID
Subscription ID identifying this subscription.See Subscription ID.
Payload
Low val
FLOAT32
0.0
Low value
High val
FLOAT32
0.0
High value
To val
FLOAT32
0.0
To value
Mask
UINT16
Monitor mask
Mask indicating which events to report
Comments
  • All payload fields except Mask are initialized to 0 and are present only for backward compatibility.
  • Successful subscription will result in an immediate response with the current value. Additional responses will be sent as the change occurs based on the Mask parameter.
  • Mask defines a filter on which events will be sent.
  • A subscription should be destroyed when no longer needed to reduce load on server. See CA_PROTO_EVENT_CANCEL.
10.1.2. Response
Table 18. Header
Command
1
Payload Size
>= 0
Size of the response.
Data Type
same as request
Payload data type.
Data Count
same as request
Payload data count.
Status code
One of ECA codes
Status code (ECA_NORMAL on success).
SubscriptionID
same as request
Subscription ID
Table 19. Payload
Values
DBR
Value stored as DBR type specified in Data Type field. See Payload Data Types.
Comments
  • Response data type and count match that of the request.
  • To confirm successful subscription, first response will be sent immediately. Additional responses will be sent as the change occurs based on mask parameters.
10.2. CA_PROTO_EVENT_CANCEL
Command
ID
2 (0x02)
Description
Clears event subscription. This message will stop event updates for specified channel. Sent over TCP.
10.2.1. Request
Table 20. Header
Command
2
Command identifier for CA_PROTO_EVENT_CANCEL.
Payload Size
0
Must be 0.
Data Type
Same value as in corresponding CA_PROTO_EVENT_ADD.
Data Count
>= 0
SID
SID of channel
SubscriptionID
Subscription ID
Comments
  • Both SID and SubscriptionID are used to identify which subscription on which monitor to destroy.
  • Actual data type and count values are not important, but should be the same as used with corresponding CA_PROTO_EVENT_ADD.
10.2.2. Response
Table 21. Header
Command
1
Command identifier for CA_PROTO_EVENT_ADD.
Payload Size
0
Must be 0.
Data Type
Same as request.
Same value as CA_PROTO_EVENT_ADD request.
Data Count
0
Must be 0.
SID
Same as request.
SubscriptionID
Same as request.
Comments
  • Notice that the response has CA_PROTO_EVENT_ADD command identifier!
  • Regardless of data type and count, this response has no payload.
10.3. CA_PROTO_READ
Command
CA_PROTO_READ
ID
3 (0x03)
Description
Read value of a channel. Sent over TCP.
Deprecated since protocol version 3.13.
10.3.1. Request
Table 22. Header
Command
3
Command identifier for CA_PROTO_READ_NOTIFY.
Payload Size
0
Must be 0.
Data Type
DBR type
Desired type of the return value.
Data Count
>= 0
Desired number of elements to read.
SID
Channel SID
SID of the channel to read.
IOID
Client provided IOID
IOID of this operation.
Comments
  • Channel from which to read is identified using SID.
  • Response will contain the same IOID as the request, making it possible to distinguish multiple responses.
10.3.2. Response
Table 23. Header
Command
3
Payload size
Size of payload
Size of DBR formatted data in payload.
Data type
DBR type
Payload format.
Data count
>= 0
Payload element count.
SID
Same as request
SID of the channel.
IOID
Same as request
Table 24. Payload
DBR formatted data
DBR
DBR formatted data
Value stored as DBR type specified in Data type field. Data count specifies number of elements of DBR value field.
10.4. CA_PROTO_WRITE
Command
CA_PROTO_WRITE
ID
4 (0x04)
Description
Writes new channel value. Sent over TCP.
10.4.1. Request
Table 25. Header
Command
CA_PROTO_WRITE
Command identifier
Payload size
Size of DBR formatted payload
Size of padded payload
Data type
DBR type
Format of payload
Data count
ELEMENT_COUNT
Number of elements in payload
SID
SID provided by server
Server channel ID
IOID
Request ID
Table 26. Payload
DBR formatted data
DBR
DBR formatted data
Comments
  • There is no response to this command.
10.5. CA_PROTO_SNAPSHOT
Command
CA_PROTO_SNAPSHOT
ID
5 (0x05)
Description
Obsolete.
10.6. CA_PROTO_BUILD
Command
CA_PROTO_BUILD
ID
7 (0x07)
Description
Obsolete.
10.7. CA_PROTO_EVENTS_OFF
Command
CA_PROTO_EVENTS_OFF
ID
8 (0x08)
Description
Disables a server from sending any subscription updates over this virtual circuit. Sent over TCP. This mechanism is used by clients with slow CPU to prevent congestion when they are unable to handle all updates received. Effective automated handling of flow control is beyond the scope of this document.
10.7.1. Request
Table 27. Header
Command
8
Command identifier for CA_PROTO_EVENTS_OFF
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Comments
  • This request will disable sending of subscription updates on the server to which it is sent.
  • Command applies to a single virtual circuit, so having multiple priority virtual circuit connections to the server would only affect the one on which the message is sent.
  • No response will be sent for this request.
10.8. CA_PROTO_EVENTS_ON
Command
CA_PROTO_EVENTS_ON
ID
9 (0x09)
Description
Enables the server to resume sending subscription updates for this virtual circuit. Sent over TCP. This mechanism is used by clients with slow CPU to prevent congestion when they are unable to handle all updates received. Effective automated handling of flow control is beyond the scope of this document.
10.8.1. Request
Table 28. Header
Command
9
Command identifier for CA_PROTO_EVENTS_ON
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Comments
  • This request will enable sending of subscription updates on the server to which it is sent.
10.9. CA_PROTO_READ_SYNC
Command
CA_PROTO_READ_SYNC
ID
10 (0x0A)
Description
10.9.1. Request
Table 29. Header
Command
10
Command identifier for CA_PROTO_READ_SYNC.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
10.10. CA_PROTO_ERROR
Command
CA_PROTO_ERROR
ID
11 (0x0B)
Description
Sends error message and code. This message is only sent from server to client in response to any request that fails and does not include error code in response. This applies to all asynchronous commands. Error message will contain a copy of original request and textual description of the error. Sent over UDP.
10.10.1. Response
Table 30. Header
Command
11
Command identifier for CA_PROTO_ERROR
Payload Size
Size of the request header that triggered the error plus size of the error message.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
CID
Channel CID
CID of the channel for which request failed.
Status Code
One of ECA codes
Error status code.
Table 31. Payload
Original Request
Message Header
Header of the request that caused the error.
Error Message
STRING
A null-terminated string conveying the error message.
Comments
  • Complete exception report is returned. This includes error message code, CID of channel on which the request failed, original request and string description of the message.
  • CID value depends on original request and may not actually identify a channel.
  • First part of payload is original request header with the same structure as sent. Any payload that was part of this request is not included. Textual error message starts immediately after the header.
10.11. CA_PROTO_CLEAR_CHANNEL
Command
ID
12 (0x0C)
Description
Clears a channel. This command will cause server to release the associated channel resources and no longer accept any requests for this SID/CID.
10.11.1. Request
Table 32. Header
Command
12
Command identifier of CA_PROTO_CLEAR_COMMAND
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
SID
SID of the channel
SID of channel to clear.
CID
CID of the channel
CID of channel to clear.
10.11.2. Response
Table 33. Header
Command
12
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
SID
Same as request
SID of cleared channel.
CID
Same as request
CID of cleared channel.
Comments
  • Server responds immediately and only then releases channel resources.
  • Once a channel with a given SID has been cleared, any request sent with this SID will fail.
  • Sent over TCP.
10.12. CA_PROTO_READ_NOTIFY
Command
ID
15 (0x0F)
Description
10.12.1. Request
Table 34. Header
Command
15
Payload Size
0
Must be 0.
Data Type
DBR type
Data Count
>= 0
SID
Channel SID
IOID
Comments
10.12.2. Response
Table 35. Header
Command
15
Payload size
Size of payload
Data type
DBR type
Payload format.
Data count
>= 0
SID
Same as request
SID of the channel.
IOID
Same as request
Table 36. Payload
DBR formatted data
DBR
DBR formatted data
10.13. CA_PROTO_READ_BUILD
Command
CA_PROTO_READ_BUILD
ID
16 (0x10)
Description
Obsolete
10.13.1. Request
10.14. CA_PROTO_CREATE_CHAN
Command
ID
18 (0x12)
Description
Requests creation of channel. Server will allocate required resources and return initialized SID. Sent over TCP.
10.14.1. Request
Table 37. Header
Command
18
Command identifier for CA_PROTO_CREATE_CHAN
Payload size
Size of payload
Padded length of channel name.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
CID
Channel CID
CID of the channel to create.
Client version
Version number
Client minor protocol version.
Payload
|[options="header"]
Name
Type
Value
Description
Channel name
STRING
Name of channel to create.
Comments
  • CID sent should be the same as used with CA_PROTO_SEARCH.
10.14.2. Response
Table 38. Header
Command
Payload size
0
Must be 0
Data type
DBR type
Native channel data type
Data count
>= 0
Native channel data count
CID
Same as request
Channel client ID
SID
Channel server ID
Comments
  • SID will be associated with CID on the server and will be reused sending certain commands that require it as a parameter.
  • SID will be valid until the channel is cleared using CA_PROTO_CLEAR or server destroys the PV the channel references.
10.15. CA_PROTO_WRITE_NOTIFY
Command
ID
19 (0x13)
Description
10.15.1. Request
Table 39. Header
Command
Command identifier
Payload size
Data type
DBR type
Format of payload
Data count
ELEMENT_COUNT
SID
Server channel ID
IOID
Request ID
Table 40. Payload
DBR formatted data
DBR
DBR formatted data
10.15.2. Response
Table 41. Header
Command
Command identifier
Payload size
0
Must be 0
Data type
Same as request
Format of data written
Data count
Same as request
Number of elements written
Status
Status code
Status of write success
IOID
Same as request
Request ID
10.16. CA_PROTO_CLIENT_NAME
Command
ID
20 (0x14)
Description
Sends local username to virtual circuit peer. This name identifies the user and affects access rights.
10.16.1. Request
Table 42. Header
Command
Command identifier
Payload size
>=0
Length of string in payload
Reserved
0
Must be 0
Reserved
0
Must be 0
Reserved
0
Must be 0
Reserved
0
Must be 0
Table 43. Payload
User name
STRING
0-terminated username string
Comments
  • This is a one-way message and will not receive response.
  • String in payload must be 0 padded to a length that is multiple of 8.
  • Sent over TCP.
10.17. CA_PROTO_HOST_NAME
Command
CA_PROTO_HOST_NAME
ID
21 (0x15)
Description
Sends local host name to virtual circuit peer. This name will affect access rights. Sent over TCP.
10.17.1. Request
Table 44. Header
Command
21
Command identifier for CA_PROTO_HOST_NAME.
Payload size
Size of payload
Length of host name string.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
Table 45. Payload
Host name
STRING
Client host name.
Comments
  • This is one-way message and will receive no response.
10.18. CA_PROTO_ACCESS_RIGHTS
Command
ID
22 (0x16)
Description
Notifies of access rights for a channel. This value is determined based on host and client name and may change during runtime. Client cannot change access rights nor can it explicitly query its value, so last received value must be stored.
10.18.1. Response
Table 46. Header
Command
22
Command identifier for CA_PROTO_ACCESS_RIGHTS.
Payload size
0
Must be 0.
Reserved
0
Must be 0.
Reserved
0
Must be 0.
CID
Channel CID
Channel affected by change.
Access Rights
Access Rights
Access rights for given channel.
Comments
  • Access Rights affect CA_PROTO_READ_NOTIFY, CA_PROTO_WRITE_NOTIFY and CA_PROTO_WRITE.
  • CA_PROTO_ACCESS_RIGHTS will be sent immediately after a channel is created using CA_PROTO_CREATE_CHAN. If they change during runtime, this message sent to report new value.
  • Changes are only sent to currently connected channels, since it requires valid CID.
  • Sent over TCP.
10.19. CA_PROTO_SIGNAL
Command
CA_PROTO_SIGNAL
ID
25 (0x19)
Description
Obsolete.
10.20. CA_PROTO_CREATE_CH_FAIL
Command
ID
26 (0x1A)
Description
Reports that channel creation failed. This response is sent to when channel creation in CA_PROTO_CREATE_CHAN fails.
10.20.1. Response
Table 47. Header
Command
Command identifier
Reserved
0
Must be 0
Reserved
0
Must be 0
Reserved
0
Must be 0
CID
Same as request
Client channel ID
Reserved
0
Must be 0
Comments
  • Sent over TCP.
10.21. CA_PROTO_SERVER_DISCONN
Command
ID
27 (0x1B)
Description
Notifies the client that server has disconnected the channel. This may be since the channel has been destroyed on server. Sent over TCP.
10.21.1. Response
Table 48. Header
Command
Command identifier
Reserved
0
Must be 0
Reserved
0
Must be 0
Reserved
0
Must be 0
CID
CID provided by client
CID that was provided during CA_PROTO_CREATE_CHAN
Reserved
0
Must be 0
11. Payload Data Types
Channel access defines special structures to transferring data. These types are organized in typed hierarchies with loose inheritance. There are six basic data types: DBR_STRING, DBR_SHORT, DBR_FLOAT, DBR_ENUM, DBR_CHAR, DBR_LONG and DBR_DOUBLE. The type DBR_INT is present as an alias for DBR_SHORT. Each of these types can represent an array of elements.
In addition to element values, some DBR types include meta-data. These types are status (DBR_STS_*), time stamp (DBR_TIME_*), graphic (DBR_GR_*) and control (DBR_CTRL_*). All these structures contain value as the last field.
All DBR data MUST be zero padded to ensure that message body length is a multiple of 8 bytes. Therefore, when receiving a message, it is necessary to use the DBR type and element count to determine the number of body bytes to use. Additional body bytes MUST be ignored.
In addition to zero padding at the end of the message, some padding is placed between the meta-data and the value array.
The following table lists the identifier, meta-data size, padding between meta-data and value, and value element sizes of each DBR type.
Table 49. DBRs
Name ID Meta size padding Element size
DBR_STRING
0
0
0
40
DBR_INT
1
0
0
2
DBR_SHORT
1
0
0
2
DBR_FLOAT
2
0
0
4
DBR_ENUM
3
0
0
2
DBR_CHAR
4
0
0
1
DBR_LONG
5
0
0
4
DBR_DOUBLE
6
0
0
8
DBR_STS_STRING
7
4
0
40
DBR_STS_INT
8
4
0
2
DBR_STS_SHORT
8
4
0
2
DBR_STS_FLOAT
9
4
0
4
DBR_STS_ENUM
10
4
0
2
DBR_STS_CHAR
11
4
1
1
DBR_STS_LONG
12
4
0
4
DBR_STS_DOUBLE
13
4
4
8
DBR_TIME_STRING
14
12
0
40
DBR_TIME_INT
15
12
2
2
DBR_TIME_SHORT
15
12
2
2
DBR_TIME_FLOAT
16
12
0
4
DBR_TIME_ENUM
17
12
2
2
DBR_TIME_CHAR
18
12
3
1
DBR_TIME_LONG
19
12
0
4
DBR_TIME_DOUBLE
20
12
4
8
DBR_GR_STRING
21
4
0
40
DBR_GR_INT
22
GR_INT
0
2
DBR_GR_SHORT
22
GR_INT
0
2
DBR_GR_FLOAT
23
GR_REAL
2
4
DBR_GR_ENUM
24
GR_ENUM
0
2
DBR_GR_CHAR
25
GR_INT
1
1
DBR_GR_LONG
26
GR_INT
0
4
DBR_GR_DOUBLE
27
GR_REAL
0
8
DBR_CTRL_STRING
28
4
0
40
DBR_CTRL_INT
29
CTRL_INT
0
2
DBR_CTRL_SHORT
29
CTRL_INT
0
2
DBR_CTRL_FLOAT
30
CTRL_REAL
0
2
DBR_CTRL_ENUM
31
GR_ENUM
0
2
DBR_CTRL_CHAR
32
CTRL_INT
1
1
DBR_CTRL_LONG
33
CTRL_INT
0
4
DBR_CTRL_DOUBLE
34
CTRL_REAL
0
8
DBR_PUT_ACKT
35
2
DBR_PUT_ACKS
36
2
DBR_STSACK_STRING
37
40
DBR_CLASS_NAME
38
40
11.1. DBR_STS_* meta-data
Alarm meta-data. Length: 4 bytes
struct metaSTS {
    epicsInt16 status;
    epicsInt16 severity;
11.2. DBR_TIME_* meta-data
Alarm and time stamp meta-data. Length: 12 bytes
struct metaTIME {
    epicsInt16 status;
    epicsInt32 secondsSinceEpoch;
    epicsUInt32 nanoSeconds;
Note that the EPICS Epoch is 1990-01-01T00:00:00Z. This is 631152000 seconds after the POSIX Epoch of 1970-01-01T00:00:00Z.
11.3. DBR_GR_SHORT meta-data
Alarm and integer display meta-data (no timestamp). Length: ?? bytes
struct metaGR_INT {
    epicsInt16 status;
    char units[8];
    epicsInt16 upper_display_limit;
    epicsInt16 lower_display_limit;
    epicsInt16 upper_alarm_limit;
    epicsInt16 upper_warning_limit;
    epicsInt16 lower_warning_limit;
    epicsInt16 lower_alarm_limit;
11.4. DBR_GR_CHAR meta-data
struct metaGR_INT {
    epicsInt16 status;
    char units[8];
    epicsInt8 upper_display_limit;
    epicsInt8 lower_display_limit;
    epicsInt8 upper_alarm_limit;
    epicsInt8 upper_warning_limit;
    epicsInt8 lower_warning_limit;
    epicsInt8 lower_alarm_limit;
11.5. DBR_GR_FLOAT meta-data
Alarm and floating point display meta-data (no timestamp). Length: ?? bytes
struct metaGR_FLOAT {
    epicsInt16 status;
    epicsInt16 precision;
    epicsInt16 padding;
    char units[8];
    epicsFloat32 upper_display_limit;
    epicsFloat32 lower_display_limit;
    epicsFloat32 upper_alarm_limit;
    epicsFloat32 upper_warning_limit;
    epicsFloat32 lower_warning_limit;
    epicsFloat32 lower_alarm_limit;
11.6. DBR_GR_DOUBLE meta-data
    epicsInt16 status;
    epicsInt16 padding;
    char units[8];
    epicsFloat64 upper_display_limit;
    epicsFloat64 lower_display_limit;
    epicsFloat64 upper_alarm_limit;
    epicsFloat64 upper_warning_limit;
    epicsFloat64 lower_warning_limit;
    epicsFloat64 lower_alarm_limit;
11.7. GR_ENUM and CTRL_ENUM meta-data
Alarm and enumerated display meta-data (no timestamp). Length: ?? bytes
struct metaGR_ENUM {
    epicsInt16 status;
    epicsInt16 number_of_string_used;
    char strings[16][26];
The strings field is an array of 16 string of 26 characters. The number_of_string_used gives the number of entries in the strings field which are valid. Additional strings should be ignored, even if they contain non-null bytes.
12. Constants
12.1. Port numbers
Although there is no requirement as to which port numbers are used by either servers or clients, there are some standard values which must be used as defaults, unless overriden by application.
Port numbers are dependant on protocol versions and are calculated using the folowing definitions:
CA_PORT_BASE = 5056
CA_SERVER_PORT = CA_PORT_BASE + MAJOR_PROTOCOL_VERSION * 2
CA_REPEATER_PORT = CA_PORT_BASE + MAJOR_PROTOCOL_VERSION * 2 + 1
Based on protocol version described in this document (4.11), port numbers used are CA_SERVER_PORT = 5064 and CA_REPEATER_PORT = 5065.
Since registration of port numbers with IANA and in the interest of compatibility, the version numbers are unlikely to change. Therefore, the port numbers described here (5064 and 5065) may be considered final.
12.2. Representation of constants
This section lists various constants, their types and values used by protocol.
Some constants can be combined using logical OR operation. Example: Monitor mask of DBE_VALUE and DBE_ALARM are combined using (DBE_VALUE or DBE_ALARM) resulting in (1 or 4 == 5).
To query the whether certain value is present in such combined value, and operation is used. Example: to query whether DBE_ALARM of monitor mask is set, (DBE_VALUE and MASK > 0) will return 0 if DBE_VALUE is not present, otherwise DBE_ALARM is present.
12.3. Monitor Mask
Indicates which changes to the value should be reported back to client library. Different values can be combined using logical OR operation.
Type: not defined, depends on the field it is in (usually UINT16)
  • DBE_VALUE - value 1 (0x01) - Value change events are reported. Value changes take into consideration a dead band within which the value changes are not reported.
  • DBE_LOG - value 2 (0x02) - Log events are reported. Similiar to DBR_VALUE, DBE_LOG defines a different dead band value that determines frequency of updates.
  • DBE_ALARM - value 4 (0x04) - Alarm events are reported whenever alarm value of the channel changes.
  • DBE_PROPERTY - value 8 (0x08) - Property events are reported when some metadata value associated with the channel changes. (Introduced in EPICS Base 3.14.11).
Notes
  • CA Servers SHOULD ignore unknown monitor mask bits.
  • Older PCAS versions will respond to unknown bits with ECA_BADMASK.
12.4. Search Reply Flag
Indicates whether server should reply to failed search messages. If a server does not know about channel name, it has the option of replying to request or ignoring it. Usually, servers contacted through address list will receive request for reply.
Type: not defined, depends on the field it is in (usually UINT16).
  • DO_REPLY - value 10 (0x0a) - Server should reply to failed search requests.
  • DONT_REPLY - value 5 (0x05) - Server should ignore failed requests.
12.5. Access Rights
Defines access rights for a given channel. Accss rights are defined as logicaly ORred value of allowed access.
  • CA_PROTO_ACCESS_RIGHT_READ - value 1 (0x01) - Read access is allowed
  • CA_PROTO_ACCESS_RIGHT_WRITE - value 2 (0x02) - Write access is allowed.
As a reference, the following values are valid.
  • 0 - No access
  • 1 - Read access only
  • 2 - Write access only
  • 3 - Read and write access
Servers MUST set undefined bits to zero. Clients MUST ignore undefined bits in this field.
13. Example message
This example shows construction of messages. For details of individual structures, see message and data type reference (CA_PROTO_READ_NOTIFY and DBR_GR_INT16).
A client will send CA_PROTO_READ_NOTIFY message with the following contents.
  • Data type: DBR_GR_INT16
  • Element count: 5
  • Server ID: 22 (obtained during channel creation)
  • Sequence ID: 56 (each read or write request increases value by one)
The messsage would be represented as follows:
00 0F (command) 00 00 (payload size) 00 16 (data type) 00 05 (element count)
00 00 00 16 (server ID) 00 00 00 38 (sequence ID)
Server would respond with success and return requested value with individual DBR_GR_INT16 fields having the following values.
  • Status: ECA_NORMAL
  • Severity: NO_ALARM (0)
00 0f (command) 00 20 (payload size) 00 16 (data type) 00 05 (element count)
00 05  00 02  43 6f 75 6e 74 73 00 00  00 0a  00 00
00 08  00 06  00 04  00 02  00 00  00 00  00 00 00 00
    8      6      4      2      0      0      0     0
14. Repeater Operation
A repeater MUST be used by clients to collect CA_PROTO_RSRV_IS_UP messages. Each client host will have one repeater.
14.1. Startup
Each client MUST test for presence of repeater on startup, before any access to EPICS hosts is made. This check is made by attempting to bind to CA_REPEATER_PORT. If binding fails, the client may assume the repeater is already running and may attempt to register. This is done by sending CA_REPEATER_REGISTER datagram to CA_REPEATER_PORT. If repeater is already active, it will respond with CA_REPEATER_CONFIRM datagram back to client. At this point the registration is complete, and the repeater will begin forwarding messages to the client.
If binding succeeds, then this client process MUST either close the bound socket (and report at error) or begin functioning as a repeater.
If an error is encountered with sending CA_REPEATER_REGISTER, the the binding test SHOULD be repeated after a short timeout (1 second is RECOMMENDED).
14.2. Client detection
The repeater SHOULD test to see if its clients exist by periodically attempting to bind to their ports. If unsuccessful when attempting to bind to the client’s port, then the repeater concludes that the client no longer exists. A technique using connected UDP sockets and ICMP destination unreachable MAY also used. If a client is determined to no longer be present then the repeater un-registers that client and no longer sends messages to it.
14.3. Operation
Each message the repeater receives MUST be forwarded to all registered clients.
14.4. Shutdown
Repeater should not shutdown on its own, if it does, there should be no active clients registered with it.
15. Searching Strategy
This section describes one possible strategy for handling CA_PROTO_SEARCH messages by a CA client. It is designed to limit the maximum rate at which search messages are sent to avoid overwhelming servers.
For each outstanding search request the following information is kept.
struct searchPV {
    const char *pvname;
    epicsTimeStamp nextSend;
    double intervalMult;
A priority queue should be maintained which is sorted in order of increasing nextSend.
When a new search request is made, a new searchPV is added to the queue with initialMult at a minimum (eg. 0.05 sec.) and nextSend at the present time plus nextSend.
When a search request is canceled it should be removed from the queue.
A task should run whenever the first entry expires (nextSend before the present time). This task should extract some expired entries up to a maximum limit (eg. enough for 4 UDP packets).
Search messages are then sent for these entries and their intervalMult is increased (eg. doubled), their nextSend is set to the present time plus nextSend, and they are re-added to the queue.
The task should then wait for the minimum search interval (eg. 0.05 sec.) before checking the queue again. This prevents a flood of search messages.
The combination of the minimum interval between sending search messages, and the limit on the maximum number of messages sent in each interval, acts to limit to total network bandwidth consumed by searches.
16. ECA Error/Status Codes
This section covers return codes and exceptions that can occur during CA command processing. In general, exceptions will be used to report various events to the application. Return codes are predefined values for conditions that can occur, where as exceptions are actually reported. Apart from exceptions that occur on server or due to network transport, additional error conditions may be reported on the client side as local exceptions.
Return codes are represented as UINT16. The 3 least significant bits indicate severity, remaining 13 bits are return code ID.
Return codes are communicated in the protocol by the CA_PROTO_READ_NOTIFY, CA_PROTO_WRITE_NOTIFY, monitor subscription responses, and the CA_PROTO_ERROR responses.
Severity codes
Code Value Description
CA_K_SUCCESS
1
Successful (not an error)
CA_K_WARNING
0
Not successful
CA_K_INFO
3
Informational (not an error)
CA_K_ERROR
2
Recoverable failure
CA_K_SEVERE
4
None recoverable failure
Presently defined error conditions
Code Severity ID Value Description
ECA_NORMAL
CA_K_SUCCESS
0
0x001
Normal successful completion
ECA_ALLOCMEM
CA_K_WARNING
6
0x030
Unable to allocate additional dynamic memory
ECA_TOLARGE
CA_K_WARNING
9
0x048
The requested data transfer is greater than available memory or EPICS_CA_MAX_ARRAY_BYTES
ECA_TIMEOUT
CA_K_WARNING
10
0x050
User specified timeout on IO operation expired
ECA_BADTYPE
CA_K_ERROR
14
0x072
The data type specifed is invalid
ECA_INTERNAL
CA_K_FATAL
17
0x08e
Channel Access Internal Failure
ECA_DBLCLFAIL
CA_K_WARNING
18
0x090
The requested local DB operation failed
ECA_GETFAIL
CA_K_WARNING
19
0x098
Channel read request failed
ECA_PUTFAIL
CA_K_WARNING
20
0x0a0
Channel write request failed
ECA_BADCOUNT
CA_K_WARNING
22
0x0b0
Invalid element count requested
ECA_BADSTR
CA_K_ERROR
23
0x0ba
Invalid string
ECA_DISCONN
CA_K_WARNING
24
0x0c0
Virtual circuit disconnect
ECA_EVDISALLOW
CA_K_ERROR
26
0x0d2
Request inappropriate within subscription (monitor) update callback
ECA_BADMONID
CA_K_ERROR
30
0x0f2
Bad event subscription (monitor) identifier
ECA_BADMASK
CA_K_ERROR
41
0x14a
Invalid event selection mask
ECA_IODONE
CA_K_INFO
42
0x153
IO operations have completed
ECA_IOINPROGRESS
CA_K_INFO
43
0x15b
IO operations are in progress
ECA_BADSYNCGRP
CA_K_ERROR
44
0x162
Invalid synchronous group identifier
ECA_PUTCBINPROG
CA_K_ERROR
45
0x16a
Put callback timed out
ECA_NORDACCESS
CA_K_WARNING
46
0x170
Read access denied
ECA_NOWTACCESS
CA_K_WARNING
47
0x178
Write access denied
ECA_ANACHRONISM
CA_K_ERROR
48
0x182
Requested feature is no longer supported
ECA_NOSEARCHADDR
CA_K_WARNING
49
0x188
Empty PV search address list
ECA_NOCONVERT
CA_K_WARNING
50
0x190
No reasonable data conversion between client and server types
ECA_BADCHID
CA_K_ERROR
51
0x19a
Invalid channel identifier
ECA_BADFUNCPTR
CA_K_ERROR
52
0x1a2
Invalid function pointer
ECA_ISATTACHED
CA_K_WARNING
53
0x1a8
Thread is already attached to a client context
ECA_UNAVAILINSERV
CA_K_WARNING
54
0x1b0
Not supported by attached service
ECA_CHANDESTROY
CA_K_WARNING
55
0x1b8
User destroyed channel
ECA_BADPRIORITY
CA_K_ERROR
56
0x1c2
Invalid channel priority
ECA_NOTTHREADED
CA_K_ERROR
57
0x1ca
Preemptive callback not enabled - additional threads may not join context
ECA_16KARRAYCLIENT
CA_K_WARNING
58
0x1d0
Client’s protocol revision does not support transfers exceeding 16k bytes
ECA_CONNSEQTMO
CA_K_WARNING
59
0x1d9
Virtual circuit connection sequence aborted
ECA_UNRESPTMO
CA_K_WARNING
60
0x1e0
Historical error conditions. Servers and clients SHOULD NOT send these codes, but MAY receive them.
ECA_MAXIOC
CA_K_ERROR
1
0x00a
Maximum simultaneous IOC connections exceeded
ECA_UKNHOST
CA_K_ERROR
2
0x012
Unknown internet host
ECA_UKNSERV
CA_K_ERROR
3
0x01a
Unknown internet service
ECA_SOCK
CA_K_ERROR
4
0x022
Unable to allocate a new socket
ECA_CONN
CA_K_WARNING
5
0x028
Unable to connect to internet host or service
ECA_UKNCHAN
CA_K_WARNING
7
0x038
Unknown IO channel
ECA_UKNFIELD
CA_K_WARNING
8
0x040
Record field specified inappropriate for channel specified
ECA_NOSUPPORT
CA_K_WARNING
11
0x058
Sorry, that feature is planned but not supported at this time
ECA_STRTOBIG
CA_K_WARNING
12
0x060
The supplied string is unusually large
ECA_DISCONNCHID
CA_K_ERROR
13
0x06a
The request was ignored because the specified channel is disconnected
ECA_CHIDNOTFND
CA_K_INFO
15
0x07b
Remote Channel not found
ECA_CHIDRETRY
CA_K_INFO
16
0x083
Unable to locate all user specified channels
ECA_DBLCHNL
CA_K_WARNING
25
0x0c8
Identical process variable name on multiple servers
ECA_ADDFAIL
CA_K_WARNING
21
0x0a8
Channel subscription request failed
ECA_BUILDGET
CA_K_WARNING
27
0x0d8
Database value get for that channel failed during channel search
ECA_NEEDSFP
CA_K_WARNING
28
0x0e0
Unable to initialize without the vxWorks VX_FP_TASK task option set
ECA_OVEVFAIL
CA_K_WARNING
29
0x0e8
Event queue overflow has prevented first pass event after event add
ECA_NEWADDR
CA_K_WARNING
31
0x0f8
Remote channel has new network address
ECA_NEWCONN
CA_K_INFO
32
0x103
New or resumed network connection
ECA_NOCACTX
CA_K_WARNING
33
0x108
Specified task isnt a member of a CA context
ECA_DEFUNCT
CA_K_FATAL
34
00x116
Attempt to use defunct CA feature failed
ECA_EMPTYSTR
CA_K_WARNING
35
0x118
The supplied string is empty
ECA_NOREPEATER
CA_K_WARNING
36
0x120
Unable to spawn the CA repeater thread- auto reconnect will fail
ECA_NOCHANMSG
CA_K_WARNING
37
0x0128
No channel id match for search reply- search reply ignored
ECA_DLCKREST
CA_K_WARNING
38
0x130
Reseting dead connection- will try to reconnect
ECA_SERVBEHIND
CA_K_WARNING
39
0x138
Server (IOC) has fallen behind or is not responding- still waiting
ECA_NOCAST
CA_K_WARNING
40
0x140
No internet interface with broadcast available
17. Example conversation
This is example conversation between client and server. Client first establishes TCP connection to the server and immediately requests creation of a channel. After server aknowledges channel creation, client reads the value of the channel twice. First as a single string value and second as a DBR_GR_INT16 type. After the response to both queries has been received, the channel is destroyed.
Client to Server
CA_PROTO_VERSION (handshake)
00 00  00 00  00 00  00 0b  00 00 00 00  00 00 00 00
    0      0      0     11            0            0
CA_PROTO_CLIENT_NAME (handshake)
00 14  00 08  00 00  00 00  00 00 00 00  00 00 00 00  61 70 75 63 65 6c 6a 00
   20      8      8      0            0            0   a  p  u  c  e  l  j \0
CA_PROTO_HOST_NAME (handshake)
00 15  00 08  00 00  00 00  00 00 00 00  00 00 00 00  63 73 6c 30 36 00 00 00
   21      8      0      0            0            0   c  s  l  0  6 \0 \0 \0
CA_PROTO_CREATE_CHAN (request)
00 12  00 18  00 00  00 00  00 00 00 01  00 00 00 0b
   18     24      0      0            1           11
61 70 75 63 65 6c 6a 3a  61 69 45 78 61 6d 70 6c 65 31 00 00 00 00 00 00
 a  p  u  c  e  l  j  :   a  i  E  x  a  m  p  l  e  1 \0 \0 \0 \0 \0 \0
Server to Client
CA_PROTO_ACCESS_RIGHTS (handshake)
00 16  00 00  00 00  00 00  00 00 00 01  00 00 00 03
   22      0      0      0            1            3
CA_PROTO_CREATE_CHAN (response)
00 12  00 00  00 06  00 01  00 00 00 01  00 00 00 04
   18      0      6      1            1            4
Client to Server
CA_PROTO_READ_NOTIFY (request)
00 0f  00 00  00 00  00 01  00 00 00 04  00 00 00 01
   15      0      0      1            4            1
00 0f  00 00  00 16  00 01  00 00 00 04  00 00 00 02
   15      0     22      1            4           02
Server to Client
CA_PROTO_READ_NOTIFY (response)
00 0f  00 08  00 00  00 01  00 00 00 01  00 00 00 01  30 00 00 00 00 06 00 01
   15      8      0      1            1            1   0
00 0f  00 20  00 16  00 01  00 00 00 01  00 00 00 02
   15     32     22      1            1           02
    5      2   C  o  u  n  t  s \0 \0     10      0
    8      6      4      2      0      0      0     0
Client to Server
CA_PROTO_CLEAR_CHANNEL (request)
00 0c  00 00  00 00  00 00  00 00 00 04  00 00 00 01
   12      0      0      0            4            1
Server to Client
CA_PROTO_CLEAR_CHANNEL (response)
   12      0      0      0            4            1
18. Glossary of Terms
IOC
Input/Output Controller.
PV
Process variable.
Virtual circuit
Reusable TCP connection between client and server, through which all PVs hosted by the server can be conveyed to the client.
19. References
ID Author Reference Revision Date Publisher
1
Jeffrey O. Hill
Channel Access Reference Manual
R3.14
2
Java Channel Access
2.0.1
3
Bradner, S.
RFC 2119: Key words for use in RFCs to Indicate Requirement Levels
1997-03