The purpose of this chapter is to describe record support in sufficient detail such that a C programmer can write new record support modules. Before attempting to write new support modules, you should carefully study a few of the existing support modules. If an existing support module is similar to the desired module most of the work will already be done.
From previous chapters, it should be clear that many things happen as a result of record processing. The details of what happens are dependent on the record type. In order to allow new record types and new device types without impacting the core IOC system, the concept of record support and device support is used. For each record type, a record support module exists. It is responsible for all record specific details. In order to allow a record support module to be independent of device specific details, the concept of device support has been created.
A record support module consists of a standard set of routines which are called by database access routines. These routines implement record specific code. Each record type can define a standard set of device support routines specific to that record type.
By far the most important record support routine is process
, which dbProcess
calls when it wants to process a record.
This routine is responsible for the details of record processing.
In many cases it calls a device support I/O routine.
The next section gives an overview of what must be done in order to process a record.
Next is a description of the entry tables that must be provided by record and device support modules.
The remaining sections give example record and device support modules and describe some global routines useful to record support modules.
The record and its device support modules are the only source files that should include the record specific header files. Thus they will be the only routines that access record specific fields without going through database access.
The most important record support routine is process
This routine determines what record processing means.
Before the record specific ``process
" routine is called, the following has already been done:
pact
must be FALSE.
The process
routine, together with its associated device support, is responsible for the following tasks:
A complication of record processing is that some devices are intrinsically asynchronous. It is NEVER permissible to wait for a slow device to complete. Asynchronous records perform the following steps:
pact = TRUE
pact = FALSE
and return
The examples given below show how this can be done.
Each record type has an associated set of record support routines.
These routines are located via the struct rset
data structure declared in recSup.h
and defined by the specific record type.
This use of a record support vector table isolates the iocCore
software from the implementation details of each record type.
Thus new record types can be defined without having to modify the IOC core software.
Each record type also has zero or more sets of device support routines. Record types without associated hardware, e.g. calculation records, normally do not have any associated device support. Record types with associated hardware normally have a device support module for each device type. The concept of device support isolates IOC core software and even record support from device specific details.
Corresponding to each record type is a set of record support routines. The set of routines is the same for every record type. These routines are located via a Record Support Entry Table (RSET), which has the following structure:
struct rset { /* record support entry table */ long number; /* number of support routine */ RECSUPFUN report; /* print report */ RECSUPFUN init; /* init support */ RECSUPFUN init_record; /* init record */ RECSUPFUN process; /* process record */ RECSUPFUN special; /* special processing */ RECSUPFUN get_value; /* OBSOLETE: Just leave NULL */ RECSUPFUN cvt_dbaddr; /* cvt dbAddr */ RECSUPFUN get_array_info; RECSUPFUN put_array_info; RECSUPFUN get_units; RECSUPFUN get_precision; RECSUPFUN get_enum_str; /* get string from enum */ RECSUPFUN get_enum_strs; /* get all enum strings */ RECSUPFUN put_enum_str; /* put enum from string */ RECSUPFUN get_graphic_double; RECSUPFUN get_control_double; RECSUPFUN get_alarm_double; };
Each record support module must define its RSET. The external name must be of the form:
<record_type>RSET
Any routines not needed for the particular record type should be initialized to the value NULL
Look at the example below for details.
Device support routines are located via a Device Support Entry Table (DSET), which has the following structure:
struct dset { /* device support entry table */ long number; /* number of support routines */ DEVSUPFUN report; /* print report */ DEVSUPFUN init; /* init support */ DEVSUPFUN init_record;/* init record instance*/ DEVSUPFUN get_ioint_info; /* get io interrupt info*/ /* other functions are record dependent*/ };
Each device support module must define its associated DSET.
The external name must be the same as the name which appears in devSup.ascii
Any record support module which has associated device support must also include definitions for accessing its associated device support modules.
The field dset
, which is declared in dbCommon
, contains the address of the DSET.
It is given a value by iocInit
This section contains the skeleton of a record support package.
The record type is xxx
and the record has the following fields in addition to the dbCommon
fields:
VAL
, PREC
, EGU
, HOPR
, LOPR
, HIHI
, LOLO
, HIGH
, LOW
, HHSV
, LLSV
, HSV
, LSV
, HYST
, ADEL
, MDEL
, LALM
, ALST
, MLST
These fields will have the same meaning as they have for the ai
record.
Consult the Record Reference manual for a description.
/* Create RSET - Record Support Entry Table*/ #define report NULL #define initialize NULL static long init_record(); static long process(); #define special NULL #define get_value NULL #define cvt_dbaddr NULL #define get_array_info NULL #define put_array_info NULL static long get_units(); static long get_precision(); #define get_enum_str NULL #define get_enum_strs NULL #define put_enum_str NULL static long get_graphic_double(); static long get_control_double(); static long get_alarm_double(); rset xxxRSET={ RSETNUMBER, report, initialize, init_record, process, special, get_value, cvt_dbaddr, get_array_info, put_array_info, get_units, get_precision, get_enum_str, get_enum_strs, put_enum_str, get_graphic_double, get_control_double, get_alarm_double }; epicsExportAddress(rset,xxxRSET); /* declarations for associated DSET */ typedef struct xxxdset { /* analog input dset */ long number; DEVSUPFUN dev_report; DEVSUPFUN init; DEVSUPFUN init_record; /* returns: (1,0)=> (failure, success)*/ DEVSUPFUN get_ioint_info; DEVSUPFUN read_xxx; }xxxdset; /* forward declaration for internal routines*/ static void checkAlarams(xxxRecord *pxxx); static void monitor(xxxRecord *pxxx);
The above declarations define the Record Support Entry Table (RSET), a template for the associated Device Support Entry Table (DSET), and forward declarations to private routines.
The RSET must be declared with an external name of xxxRSET
. It defines the record support routines supplied for this record type.
Note that forward declarations are given for all routines supported and a NULL
declaration for any routine not supported.
The template for the DSET is declared for use by this module.
static long init_record(void *precord, int pass) { xxxRecord*pxxx = (xxxRecord *)precord; xxxdset*pdset; longstatus; if(pass==0) return(0); if((pdset = (xxxdset *)(pxxx->dset)) == NULL) { recGblRecordError(S_dev_noDSET,pxxx,"xxx: init_record"); return(S_dev_noDSET); } /* must have read_xxx function defined */ if( (pdset->number < 5) || (pdset->read_xxx == NULL) ) { recGblRecordError(S_dev_missingSup,pxxx, "xxx: init_record"); return(S_dev_missingSup); } if( pdset->init_record ) { if((status=(*pdset->init_record)(pxxx))) return(status); } return(0); }
This routine, which is called by iocInit
twice for each record of type xxx
, checks to see if it has a proper set of device support routines and, if present, calls the init_record
entry of the DSET.
During the first call to init_record
(pass=0) only initializations relating to this record can be performed.
During the second call (pass=1) initializations that may refer to other records can be performed.
Note also that during the second pass, other records may refer to fields within this record.
A good example of where these rules are important is a waveform record.
The VAL
field of a waveform record actually refers to an array.
The waveform record support module must allocate storage for the array.
If another record has a database link referring to the waveform VAL
field then the storage must be allocated before the link is resolved.
This is accomplished by having the waveform record support allocate the array during the first pass (pass=0) and having the link reference resolved during the second pass (pass=1).
static long process(void *precord) { xxxRecord*pxxx = (xxxRecord *)precord; xxxdset*pdset = (xxxdset *)pxxx->dset; longstatus; unsigned char pact=pxxx->pact; if( (pdset==NULL) || (pdset->read_xxx==NULL) ) { /* leave pact true so that dbProcess doesnt call again*/ pxxx->pact=TRUE; recGblRecordError(S_dev_missingSup,pxxx,"read_xxx"); return(S_dev_missingSup); } /* pact must not be set true until read_xxx completes*/ status=(*pdset->read_xxx)(pxxx); /* read the new value */ /* return if beginning of asynch processing*/ if(!pact && pxxx->pact) return(0); pxxx->pact = TRUE; recGblGetTimeStamp(pxxx); /* check for alarms */ alarm(pxxx); /* check event list */ monitor(pxxx); /* process the forward scan link record */ recGblFwdLink(pxxx); pxxx->pact=FALSE; return(status); }
The record processing routines are the heart of the IOC software.
The record specific process routine is called by dbProcess
whenever it decides that a record should be processed.
Process decides what record processing really means.
The above is a good example of what should be done.
In addition to being called by dbProcess
the process routine may also be called by asynchronous record completion routines.
The above model supports both synchronous and asynchronous device support routines.
For example, if read_xxx
is an asynchronous routine, the following sequence of events will occur:
process
is called with pact
FALSE
read_xxx
is called.
Since pact
is FALSE
it starts I/O, arranges callback, and sets pact
TRUE
read_xxx
returns
pact
went from FALSE
to TRUE
process just returns
dbProcess
is ignored because it finds pact
TRUE
process
is called again.
read_xxx
is called.
Since pact
is TRUE
it knows that it is a completion request.
read_xxx
returns
process
completes record processing
pact
is set FALSE
process
returns
At this point the record has been completely processed.
The next time process
is called everything starts all over from the beginning.
static long get_units(DBADDR *paddr, char *units) { xxxRecord *pxxx=(xxxRecord *)paddr->precord; strncpy(units,pxxx->egu,sizeof(pxxx->egu)); return(0); } static long get_graphic_double(DBADDR *paddr, struct dbr_grDouble *pgd) { xxxRecord *pxxx=(xxxRecord *)paddr->precord; int fieldIndex = dbGetFieldIndex(paddr); if(fieldIndex == xxxRecordVAL) { pgd->upper_disp_limit = pxxx->hopr; pgd->lower_disp_limit = pxxx->lopr; } else recGblGetGraphicDouble(paddr,pgd); return(0); } /* similar routines would be provided for */ /* get_control_double and get_alarm_double*/
These are a few examples of various routines supplied by a typical record support package. The functions that must be performed by the remaining routines are described in the next section.
static void checkAlarms(xxxRecord *pxxx) { double val; float hyst,lalm,hihi,high,low,lolo; unsigned short hhsv,llsv,hsv,lsv; if(pxxx->udf == TRUE ){ recGblSetSevr(pxxx,UDF_ALARM,VALID_ALARM); return; } hihi=pxxx->hihi; lolo=pxxx->lolo; high=pxxx->high; low=pxxx->low; hhsv=pxxx->hhsv; llsv=pxxx->llsv; hsv=pxxx->hsv; lsv=pxxx->lsv; val=pxxx->val; hyst=pxxx->hyst; lalm=pxxx->lalm; /* alarm condition hihi */ if (hhsv && (val >= hihi || ((lalm==hihi) && (val >= hihi-hyst)))) { if(recGblSetSevr(pxxx,HIHI_ALARM,pxxx->hhsv) pxxx->lalm = hihi; return; } /* alarm condition lolo */ if (llsv && (val <= lolo || ((lalm==lolo) && (val <= lolo+hyst)))) { if(recGblSetSevr(pxxx,LOLO_ALARM,pxxx->llsv)) pxxx->lalm = lolo; return; } /* alarm condition high */ if (hsv && (val >= high || ((lalm==high) && (val >= high-hyst)))) { if(recGblSetSevr(pxxx,HIGH_ALARM,pxxx->hsv)) pxxx->lalm = high; return; } /* alarm condition low */ if (lsv && (val <= low || (lalm==low) && (val <= low+hyst)))) { if(recGblSetSevr(pxxx,LOW_ALARM,pxxx->lsv)) pxxx->lalm = low; return; } /*we get here only if val is out of alarm by at least hyst*/ pxxx->lalm=val; return; }
This is a typical set of code for checking alarms conditions for an analog type record. The actual set of code can be very record specific. Note also that other parts of the system can raise alarms. The algorithm is to always maximize alarm severity, i.e. the highest severity outstanding alarm will be reported.
The above algorithm also honors a hysteresis factor for the alarm. This is to prevent alarm storms from occurring in the event that the current value is very near an alarm limit and noise makes it continually cross the limit. It honors the hysteresis only when the value is going to a lower alarm severity.
Note the test:
Database common defines the field UDF, which means that field VAL is undefined.
The STAT and SEVR fields are initialized as though recGblSetSevr(pxxx,UDF_ALARM,VALID_ALARM)
was called.
Thus if the record is never processed the record will be in an INVALID UNDEFINED alarm state.
Field UDF is initialized to the value 1, i.e. TRUE.
Thus the above code will keep the record in the INVALID UNDEFINED alarm state as long as UDF is not given the value 0.
The UDF field means Undefined, i.e. the VAL field has never been given a value. When records are loaded into an ioc this is the initial state of records. Whevever code gives a value to the VAL field it is also supposed to set UDF false. Unless a particular record type has unusual semantics no code should set UDF true. UDF normally means that the field was never given a value.
For input records device support is responsible for obtaining an input value. If no input value can be obtained neither record support nor device support sets UDF false. If device support reads a raw value it returns a value telling record support to perform a conversion. After the record support sets VAL equal to the converted value, it sets UDF false. If device support obtains a converted value that it writes to VAL, it sets UDF false.
For output records either something outside record/device support writes to the VAL field or else VAL is given a value because record support obtains a value via the OMSL field. In either case the code that writes to the VAL field sets UDF false.
Whenever database access writes to the VAL field it sets UDF false.
Routine recGblSetSevr is called to raise alarms. It can be called by iocCore, record support, or device support. The code that detects an alarm is responsible for raising the alarm.
static void monitor(xxxRecord *pxxx) { unsigned short monitor_mask; float delta; monitor_mask = recGblResetAlarms(pxxx); /* check for value change */ delta = pxxx->mlst - pxxx->val; if(delta<0.0) delta = -delta; if (delta > pxxx->mdel) { /* post events for value change */ monitor_mask |= DBE_VALUE; /* update last value monitored */ pxxx->mlst = pxxx->val; } /* check for archive change */ delta = pxxx->alst - pxxx->val; if(delta<0.0) delta = 0.0; if (delta > pxxx->adel) { /* post events on value field for archive change */ monitor_mask |= DBE_LOG; /* update last archive value monitored */ pxxx->alst = pxxx->val; } /* send out monitors connected to the value field */ if (monitor_mask){ db_post_events(pxxx,&pxxx->val,monitor_mask); } return; }
All record types should call recGblResetAlarms
as shown.
Note that nsta
and nsev
will have the value 0 after this routine completes.
This is necessary to ensure that alarm checking starts fresh after processing completes.
The code also takes care of raising alarm monitors when a record changes from an alarm state to the no alarm state.
It is essential that record support routines follow the above model or else alarm processing will not follow the rules.
Analog type records should also provide monitor and archive hysteresis fields as shown by this example.
db_post_events
results in channel access issuing monitors for clients attached to the record and field.
The call is
int db_post_events(void *precord, void *pfield, unsigned int monitor_mask)where:
precord
- The address of the record
pfield
- The address of the field
monitor_mask
- A bit mask that can be any combinations of the following:
recGblResetAlarms
db_post_event
for any fields that change as a result of record processing.
Also it should NOT call db_post_event
for fields that do not change.
This section describes the routines defined in the RSET.
Any routine that does not apply to a specific record type must be declared NULL
long report(void *precord);
This routine is not used by most record types. Any action is record type specific.
long initialize(void);
This routine is called once at IOC initialization time. Any action is record type specific. Most record types do not need this routine.
long init_record(void *precord, int pass);
iocInit
calls this routine twice (pass=0 and pass=1) for each database record of the type handled by this routine.
It must perform the following functions:
long process(void *precord);
This routine must follow the guidelines specified previously.
long special(struct dbAddr *paddr, int after);
This routine implements the record type specific special processing for the field referred to by dbAddr
It is called twice when a field is written to from outside the record, once with after=0 before any changes are made to the field, and again with after=1 after the change has been made.
The routine can prevent any changes from being made by returning an error status from the first call (after=0).
File special.h
defines special types.
This routine is only called for user special fields, i.e. fields with SPC_xxx
>= 100.
A field is declared special in the ASCII record definition file.
New values should not by added to special.h
, instead use SPC_MOD
The database access routine, dbGetFieldIndex
can be used to determine which field is being modified.
This routine is no longer used. It should be left as a NULL procedure in the record support entry table.
long cvt_dbaddr(struct dbAddr *paddr);
This routine is called by dbNameToAddr
if the field has special set equal to SPC_DBADDR
A typical use is when a field refers to an array.
This routine can change any combination of the dbAddr
fields:
no_elements
, field_type
, field_size
, special,pfield,
and dbr_type
For example if the VAL
field of a waveform record is passed to dbNameToAddr
, cvt_dbaddr
would change dbAddr
so that it refers to the actual array rather then VAL
NOTES:
db_name_to_addr
, which is part of old database access.
db_name_to_addr
calls dbNameToAddr
This is done when a client connects to the record.
long get_array_info(struct dbAddr *paddr, long *no_elements, long *offset);
This routine returns the current number of elements and the offset of the first value of the specified array. The offset field is meaningful if the array is actually a circular buffer.
It is permissible for get_array_info
to change pfield
This feature can be used to implement double buffering.
When an array field is being written get_array_info
is called before the field values are changed.
long put_array_info(struct dbAddr *paddr, long nNew);
This routine is called after new values have been placed in the specified array.
long get_units(struct dbAddr *paddr, char *punits);
This routine sets units equal to the engineering units for the field.
long get_precision(struct dbAddr *paddr, long *precision);
This routine gets the precision, i.e.
number of decimal places, which should be used to convert the field value to an ASCII string.
recGblGetPrec
should be called for fields not directly related to the value field.
long get_enum_str(struct dbAddr *paddr, char *p);
This routine sets *p
equal to the ASCII string for the field value.
The field must have type DBF_ENUM
Look at the code for the bi
or mbbi
records for examples.
long get_enum_strs(struct dbAddr *paddr, struct dbr_enumStrs *p);
This routine gives values to all fields of structure dbr_enumStrs
or mbbi
long put_enum_str(struct dbAddr *paddr, char *p);
Given an ASCII string, this routine updates the database field. It compares the string with the string values associated with each enumerated value and if it finds a match sets the database field equal to the index of the string which matched.
or mbbi
long get_graphic_double(struct dbAddr *paddr, struct dbr_grDouble *p);
This routine fills in the graphics related fields of structure dbr_grDouble
long get_control_double(struct dbAddr *paddr, struct dbr_ctrlDouble *p);
This routine gives values to all fields of structure dbr_ctrlDouble
recGblGetControlDouble
long get_alarm_double(struct dbAddr *paddr, struct dbr_alDouble *p);
This routine gives values to all fields of structure dbr_alDouble
A number of global record support routines are available. These routines are intended for use by the record specific processing routines but can be called by any routine that wishes to use their services.
The name of each of these routines begins with ``recGbl
Code using these routines should
#include <recGbl.h>
Alarms may be raised in many different places during the course of record processing.
The algorithm is to maximize the alarm severity, i.e. the highest severity outstanding alarm is raised.
If more than one alarm of the same severity is found then the first one is reported.
This means that whenever a code fragment wants to raise an alarm, it does so only if the alarm severity it will declare is greater then that already existing.
Four fields (in database common) are used to implement alarms:
sevr
, stat
, nsev
, and nsta
The first two are the status and severity after the record is completely processed.
The last two fields (nsta
and nsev
) are the status and severity values to set during record processing.
Two routines are used for handling alarms.
Whenever a routine wants to raise an alarm it calls recGblSetSevr
This routine will only change nsta
and nsev
if it will result in the alarm severity being increased.
At the end of processing, the record support module must call recGblResetAlarms
This routine sets stat = nsta
, sevr = nsev
, nsta= 0
, and nsev = 0
If stat
or sevr
has changed value since the last call it calls db_post_event
for stat
and sevr
and returns a value of DBE_ALARM
If no change occured it returns 0.
Thus after calling recGblResetAlarms
everything is ready for raising alarms the next time the record is processed.
The example record support module presented above shows how these macros are used.
int recGblSetSevr(void *precord, short nsta, short nsevr);
Returns TRUE
if it changed nsta
and/or nsev
, FALSE
if it did not change them.
unsigned short recGblResetAlarms(void *precord);
Returns: Initial value for monitor_mask
Database common contains two additional alarm related fields:
acks
- highest severity unacknowledged alarm
ackt
- do transient alarm need to be acknowledged
These fields are handled by iocCore
and recGblResetAlarms
and should not be used by record support.
The alarm acknowledgement facility it provided for use by alarm handlers.
SUGGESTION: use errlogPrintf
instead of this for new code.
void recGblDbaddrError( long status, struct dbAddr *paddr, char *pcaller_name); /* calling routine name */
This routine interfaces with the system wide error handling system to display the following information: Status information, process variable name, calling routine.
void recGblRecordError( long status, void *precord, char *pcaller_name); /* calling routine name */
This routine interfaces with the system wide error handling system to display the following information: Status information, record name, calling routine.
void recGblRecsupError( long status, struct dbAddr *paddr, char *pcaller_name, /* calling routine name */ char *psupport_name); /* support routine name*/
This routine interfaces with the system wide error handling system to display the following information: Status information, record name, calling routine, record support entry name.
void recGblGetGraphicDouble(struct dbAddr *paddr, struct dbr_grDouble *pgd);
This routine can be used by the get_graphic_double
record support routine to obtain graphics values for fields that it doesn't know how to set.
void recGblGetControlDouble(struct dbAddr *paddr, struct dbr_ctrlDouble *pcd);
This routine can be used by the get_control_double
record support routine to obtain control values for fields that it doesn't know how to set.
void recGblGetAlarmDouble(struct dbAddr *paddr, struct dbr_alDouble *pcd);
This routine can be used by the get_alarm_double
void recGblGetPrec(struct dbAddr *paddr, long *pprecision);
This routine can be used by the get_precision
record support routine to obtain the precision for fields that it doesn't know how to set the precision.
void recGblGetTimeStamp(void *precord)
This routine gets the current time stamp and puts it in the record It does the following:
epicsTimeEventDeviceTime
(-2) then noting is done, i.e. the routine just returns.
epicsTimeGetEvent
is called.
void recGblFwdLink(void *precord);
This routine can be used by process to request processing of forward links.
int recGblInitConstantLink( struct link *plink, short dbfType, void *pdest);
Initialize a constant link.
This routine is usually called by init_record
(or by associated device support) to initialize the field associated with a constant link.
It returns(FALSE, TRUE) if it (did not, did) modify the destination.
void recGblCheckDeadband( epicsFloat64 *poldval, const epicsFloat64 newval, const epicsFloat64 deadband, unsigned *monitor_mask, const unsigned add_mask);
Check if analog (double) value is outside specified deadband, and set bits in monitor mask.
This routine is usually called by an analog record's monitor
(as part of processing) to check if a value is outside a predefined deadband.
It also set bits in a monitor mask according to the check result.
If newval
lies outside the specified deadband
, newval
is copied into *poldval
, and add_mask
is OR'ed into monitor_mask
